What is meant by Active and reactive power?
Answer Posted / naresh
Description
The Active & Reactive Power block measures the active power P and reactive power Q associated with a periodic voltage-current pair that can contain harmonics. P and Q are calculated by averaging the V I product with a running average window over one cycle of the fundamental frequency, so that the powers are evaluated at fundamental frequency.
| Is This Answer Correct ? | 6 Yes | 5 No |
Post New Answer View All Answers
what is the purpose of high speed earth switch in gas insulated substat
Witch do depand of Power factor and theory of power factor?
what are the standard IR values should be of R-E, Y-E, B-E, R-Y, Y-B, B-R of VCB in closed condition and in open condition for 500KVA & 1000KVA transformers. and what is the acceptable range when tested by 5000V megger.
How to use computer cpu ups use for home inverter circuit board
which is better to use svc or synchronous condenser why ?
No load tap changing transformer working
Why temperature rise is conducted in bus bars and isolators?
i am studying in final year can i allowed for 23rd UES of Indian army
List advantges of active filter over passive filter?
how to calculate slip ring induction motor stator and rotor currents??
what is load despatching
Define maximum demand?
Swg formulae
What should be the magnetic balance test values for a 3 phase delta/star connected single primary dual secondary winding transformer (90 MVA / 2 X 45 MVA TRANSFORMER)
What information we need to prepare relay coordination chart