Difference between ups and invertor

Answer Posted / aravind bandaru

While both provide backup power during mains outage, with
the UPS the switch is instantaneous whereas with the
Inverter there is a gap of a second or two. This gap is OK
for household gadgets such as lights, fans, fridge, etc.
but not OK for computers.

In technical terms:

UPS: The mains power comes to the UPS. The AC is converted
to DC and this DC is constantly charging the battery. The
output of the battery is fed to the Sine wave inverter and
it converts DC to AC and this feeds the equipment. Since
power out is always drawn from the battery, there is no
time lag when mains swicthes off; it justs stops the
battery from being charged and the UPS continues to supply
power till the battery runs out.

Inverter: The mains power comes to the Inverter. This is
directly sent to the output but the AC is also converted to
DC and this DC is constantly charging the battery. A sensor
and relay mechanism checks whether the mains is ON or OFF.
When the main switches OFF, the relay actuator triggers to
switch from mains to inverter. Rest is same like the UPS.
Because of this sensor and relay, there is a gap between
triggering.

Is This Answer Correct ?    6 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Why we specify TNC switch with 1NO 1NC ,2NO 2NC ? how we get connection.?

1269


how power trnafor from 1 point to another point in bus bar ya transmission line( voltage trnasfer from 1 point to another poin)

1497


What are the weight of 800KV DA,DB and DC type tower ?

2711


What is effect on in zone and out zone fault if CT chosen for phase side is Vk/2<5mA and Neutral side is Vk/2<15mA on REF protection of Transformer

1906


how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?

1408






Define peak time.

693


Why insulation level follows this order? transformer < bus bar < circuit breaker & Isolator < transmission line.

1690


State uses of different types of stsrters with different capacities of motors as below: a. up to 5HP b. above 5hp to 10hp c. above 10hp to 20hp d. above 20hp

1477


Brief working principle of stabilizer,application & safety precautions

5159


What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.

1634


What Should be the value of Vector Surge angle at Tripping and how to calculate it?

1595


What is the Diff. btw Manule Pull Station & Manule Abort Station Switches used in FM200 System??

1397


The series field winding has low resistance while the shunt field winding has high resistance. Why?

1242


If two Transformers are connected in parallel having impedance of 50KA in both transformers will the impedance increase or decrease after connecting transformers in parallel?

1543


what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks

1747