What is difference between earth leakage relay and
restricted earth fault relay ?
Answer Posted / s. malhotra
Restricted EF relay is meant for sensing earth fault/
leakage current in a "restricted zone", a zone bound by the
2 sets of Current transformers - one set at the beginning of
the zone and one at its end.
There is NO particular zone restriction for the normal Earth
leakage relay which will sense an earth fault or earth
leakage downstream of it. Though you may call the entire
downstream as a zone, in comparison to the REF it is left
unqualified
| Is This Answer Correct ? | 23 Yes | 3 No |
Post New Answer View All Answers
what is meant by skew width in machines?
What is the difference between security constraint unit commitment and security constraint optimal power flow?
What will be result if we connect LT votage to the terminal of HT motor?
Transformer how to maintaince a check b check c check d check
How you calculate the repturing capacity of a HRC fuse
what is the min and max ohmic resistance for the earthing rod installed for lighting poles for street light network
stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate
What is the principal of motor?
please give me all the Alarm .Trip ,Safety Relays & Conditions of Diesel-generators mail me on ashokbabunhce@gmail.com
can you please send me the technical questions and aptitude questions of honeywell and jindal steel electrical engg. question paper my e-mail ID is(kkesavanraj@gmail.com)
PLEASE SEND THE PREVIOUS YEARS QUESTION PAPERS OF RRB JUNIOR ENGINEER-ELECTRICAL
Difference between rating factor of cable and derating factor of cable?
How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?
What is dielectric loss?
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?