synchronous motor of 13.5MW having which type protection?
and how to set relay?give me relay setting calculation for
different protection for this motor assume efficiency,power
factor and other term if neccecery
Answer Posted / ravi
Protection of S.M Above 12 MW:-
The Best Protection method is by SPM:-
Application of SPM Protection:-
• Field application
• DC field current loss, exciter current loss, DC field
voltage
check
• PF regulation, reluctance torque synchronizing
• Protects motor during start up and in the event of
asynchronous operation
• Squirrel cage winding overheating protection
• Automatic phase rotation correction
• Auto-loading and incomplete sequence
• Regulator tuning mode
• True RMS metering with DFT filtering
• Optional power factor regulator with adjustable settings
• Power factor & pull out protection (Optional)
• Speed dependent squirrel cage overload protection
• Motor restart protection
| Is This Answer Correct ? | 3 Yes | 1 No |
Post New Answer View All Answers
Direction of flow of active power and reactive power with logic?
induction 3 phase motor terminal connection
What is vaccum currcuit breaker.define with cause and where be use it device?
What would cause a 240v choke that should give 110v out on a 16w lamp to gradually increase to 160v?
we have two motors 1250kW,6.6kV to be coupled on the same shaft ,so please provide assistance for their synchronisation.
The transmission does not have options: a)Partition noise b) Flicker noise c) resistance d) Short noise and reason
how we calculate electrical load on a building according to area?
hi, could someone help me to find a control design for syncronising panel .
what are the precuation should be taken ahen installing power transformer,circuit breaker,current & potential transformer
How do you calculate the actual power consumption of an inductive load appliance. Say, a deep freezer of 200watts
Do closed loops systems require manual input?
what is the effect of back reactive power on the generator ?
how to calculate current carring capacity of cable and cable selection? 1) copper flexible cable 2) copper armoured cable 3) Aluminium cable
what is the path of thunderlightening? once both a buffalo and a person were standing 5m apart but lightening hit and killed buffalo not person?
i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?