What is the required bending radius requied at the time of
cable laying?

Answer Posted / vknt

bending radius should be 12 to 15 times of the cable diameter.
for XLPE cable 12 times of dia.
for PILC cable 15 times of dia.

Is This Answer Correct ?    11 Yes 5 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!

1317


why ss stablity limit is more transient stablity limit?

1671


Why the efficiency of a three-phase induction is the motor is less than that of a three-phase transformer?

726


What is the formula of frequency ?

972


How many types of electric motors are there?

660






What is PQA???Applications........

1897


What is vacuum circuit breaker.define with cause and where be use it device?

741


What is inrush current?

651


At the starting of dc motor and syn.motor and induction motor high current flowing through the winding. Due to this the windings burnt out. To avoid this different types of starters are used. But incase of transformer what Will be used (At starting no emf is induced in the primary winding)?

1552


Draw a block diagramof Three UPS systems connected in Parallel mode?

1681


How to calculate the time setting for star connection in star delta starter? For example 10KW 3PH Induction motor.

2164


What is different between Difnit time and instatous over current relay

1991


what will happen if earth of 33 kv cable (earthed system) is not connected to earthing pit?

1549


Briefly describe means used by electricity suppliers to influence the flow of active and reactive power in power networks (one for each type)?

1516


what is size of 3phase 4wire cable to be used for 11 ton ductable A.C and how to calculate cable size for different load

3600