what is the CT of protection and CT of metering ? what is
class 5P10 & 5P20 and class PS ?

Answer Posted / duraivelu j

there are two type of ct. one is metering ( class 0.1,class
0.5,1,&5)another one is Protection (PS, 5P10,5P20)the
metering ct has very less error, so we can measure actual
power by accuratly,the protecton ct has more error but that
has more saturaion level, so during fault condition this ct
will not saturate. bur Metering ct will saturate when fault
condition and that time we can't measure the current vale.

Is This Answer Correct ?    183 Yes 17 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Starting Time of LT & HT Motor

1489


why we can use 1 to 5V dc

1518


how do i work out the Amps of a incommer if i am running 1 37 KW motor and a 0,75 KW motor and some solinoids

1428


Starting times for soft starter & power factor is thier any standard or datas available in manufactures list. Kindly suggest.

1469


what is the maximum temperature rating of a thhn insulated conductor?

1364






Why the arms of delta in a delta-wye power transmission system are kept constant??

1419


WHAT IS THE MEANING OF BALANCED / UNBALANCED IN STABILIZER TYPES.

1974


how to calculate transformer load?

1955


What are all present producing cost of Per KWH of various Fuel?

2121


what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?

1538


at which voltage level arcing ground is occurs ??????????

1585


hi friends if you have any 400KV Substation Erection and installations Drgs please send to me.My email id:kandi.suresh441@gmail.com

2400


how the inner and outer body is separated in aircrafts?

598


Power Factor Correction Panel (Manual & Automatic)

1695


Difference between HRG and NGR. Are they both the same thing

3671