Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what is the CT of protection and CT of metering ? what is
class 5P10 & 5P20 and class PS ?

Answer Posted / duraivelu j

there are two type of ct. one is metering ( class 0.1,class
0.5,1,&5)another one is Protection (PS, 5P10,5P20)the
metering ct has very less error, so we can measure actual
power by accuratly,the protecton ct has more error but that
has more saturaion level, so during fault condition this ct
will not saturate. bur Metering ct will saturate when fault
condition and that time we can't measure the current vale.

Is This Answer Correct ?    183 Yes 17 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

For high frequency application we use which transformer?

1934


What is class ab operation?

1059


What is reactance, reluctance,capistance, pls give answeer in hinglish and be simply Jo asani we smajh m aa jaye

2118


internally connection of photvoltic module

1929


How to use earthing on shipments.

1446


which capacity of RCCB used for five thousand watt electricity load?

1874


Air circuit breaker safety

1425


i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.

2346


how to setting voltage RTCC panel

1675


Single line digram for 11 kV to distribution use go,la and do

1822


How to checked frequency drive output voltages?

1198


how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!

2340


CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415

2657


How i can calculate current of cable according to ares?

2004


How many devices can be connected in one zone of FACP

2323