what is the CT of protection and CT of metering ? what is
class 5P10 & 5P20 and class PS ?
Answer Posted / duraivelu j
there are two type of ct. one is metering ( class 0.1,class
0.5,1,&5)another one is Protection (PS, 5P10,5P20)the
metering ct has very less error, so we can measure actual
power by accuratly,the protecton ct has more error but that
has more saturaion level, so during fault condition this ct
will not saturate. bur Metering ct will saturate when fault
condition and that time we can't measure the current vale.
| Is This Answer Correct ? | 183 Yes | 17 No |
Post New Answer View All Answers
For high frequency application we use which transformer?
What is class ab operation?
What is reactance, reluctance,capistance, pls give answeer in hinglish and be simply Jo asani we smajh m aa jaye
internally connection of photvoltic module
How to use earthing on shipments.
which capacity of RCCB used for five thousand watt electricity load?
Air circuit breaker safety
i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.
how to setting voltage RTCC panel
Single line digram for 11 kV to distribution use go,la and do
How to checked frequency drive output voltages?
how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
How i can calculate current of cable according to ares?
How many devices can be connected in one zone of FACP