what is difference between AC VVVF drive & Dc VVVF drive
explain their working principle?
Answer Posted / sanjeev
There is nothing like DC VVVF Drive,and AC vvvf drives
control it's output through it variable frequency,we can't
check the voltage at motor with multimeter,and IGBT for
speed reference does two works,speed and during stop or
braking the regenrated voltage thrown to it's incoming
itself hence saves power.
| Is This Answer Correct ? | 25 Yes | 0 No |
Post New Answer View All Answers
what are the safety measures of induction motor?
Name one of major transformer company in KSA ?
What are the temperature elements?
What are the factor to be consider for CT selection in 132kV substation?
What are the effects of adding a zero to a system?
How to test IR testing & magnetic balance test
stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate
i have 3500 amp load and select current transformer and perches.how i calculate .please understand
What is notching in dc machine?
Why do we need interlocking in a HT metering or Ring main unit switchgear?
advantages & disadvantages of Lagging and leading power factor .
How do you determine the size of transformer radiators in a transformer?
Is it possible to download the Siemens Selection Chart(TYPE 2 coordination) for 1) fuseless selection 2)Fuse selection
need to make a report. Need to choose a 3phase induction motor. Load conditions motor will operate in : Maximum Load: 30 Kw Speed: 2950 rpm Ambient temp: 20 cent Supply voltage: 440V Frequency: 50Hz need to look for the safety factor when choosing the motor, went through catalouge found a few, but dont know how to choose the safety factor allowing an extra load something above 30 KW to avoid any harm.
how to select rating of HT Panel