3. What is Impedance Voltage in Transformer?
Answer Posted / ravi
Impedance voltage of a transformer is the voltage required
to
short circuit the secondary winding terminals of the
transformer and apply voltage gradually from zero at
primary winding.increase the voltage gradullay till the
full load current flows in the secondary.The voltage at
which full load current flows that voltage is the impedance
voltage of the transformer.This is required for short
circuit calculations.You can find on the transformer name
plate as Impedance voltage or percentage impedance.
| Is This Answer Correct ? | 287 Yes | 23 No |
Post New Answer View All Answers
how to store the thunder power?
The moisture in air will condense at
Where is servomechanism used?
Comment on the working principle of operation of a single-phase transformer.
why we can use 1 to 5V dc
Distribution transformer we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral,we can not connect separate body earthing pit to other earthing pit but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), is this safe for transformer and other equipment?
On Which Pressure PRV is operated.
A 11KV, 1200 A breaker combination fixed in a cubicle for HT motor.Is normally for 11 KV motor fuse is using? if Yes, What range fuse is required?
What is q factor?
How to find ampere on ht side for selection of cable size ???
why power factor is important?
which is better to use svc or synchronous condenser why ?
role of europe union in UK safety legistlation (electrical safety)
Dear Mr B C pal...Can you plz. put some light on principle of operation of Z-Ct in conjunction to its use with 1Cx1000Sqmm HT Cables & Directional Ground Fault / Over Voltage Relays...Regd..Parag v K 9899115632
What is BusBar integrity test and how it is conducted?