What core magnetic balance test of transformer?
How to do this test in a three phase Star delta (star-LV,
Delta-HV) transformer?
How to measure and where to measure?
thanks and regards
Austin
Answer Posted / rajukumar sripelli
HI ,
this is rajukumar sripelli from REPUTED TRANSFORMER
MANUFACTURING COMPANY ..testing department ..
AS u all above is not fully correct....
Magnetic balance test is done on TRANSFORMER to see whether
the transformer core is magnetically balanced or
not...AND ALSO WINDING CONDITION....IN FAULT CONDITION DUE
TO HIGH CURRENTS WINDING MAY BE DAMAGE....
for example
we r having delta HV and star winding LV side ...
HV SIDE WE WIL BE HAVING THREE BUSHINGS....THOSE R 1U,1V,1W..
HV SIDE WE WIL BE HAVING FOUR BUSHINGS.....2U,2V,2W,2N...
WE CAN DO THIS MBT (MAGNETIC BALANCE TEST)WITH 1PHASE
SUPPLY(1PHASE AND NEUTRAL(230V)) OR WITH 2-PHASE
SUPPLY(2-PHASES(440V))
1ST STEP OF MBT: GIVE POWER SUPPLY 1-PHASE OR 2 PHASE
BETWEEN 1U AND 1V ,MEASURE THE VOLTAGES BETWEEN 1V-1W AND
1U-1W AND ALSO 2U-2N,2V-2N,2W-2N..
SO HERE IF THE CORE IS CORRECTLY BALANCED THEN WE WILL GET
RESULTS AS FOLLOWS
1U-1V 1V-1W 1U-1W 2U-2N 2V-2N 2W-2N
440 300 140 90 50 40
THAT MEANS HV SIDE : 1U-1V = 1V-1W + 1U-1W
I.E 440V = 300 + 140
AND ALSO LV SIDE : 2U-2N = 2V-2N + 2W-2N
90 = 50 + 40
STEP 2: AFTER DOING THIS ..INTERCHANGE THE CONNECTIONS
BETWEEN 1V-1W AND MEASURE THE VALUES AS ABOVE...
STEP 3: AFTER DOING THIS ..INTER CHANGE THE CONNECTIONS
BETWEEN 1U-1W AND MEASURE THE VALUES AS ABOVE...
IF ANY FAULT IS THERE IN TRANSFORMER WE CAN NOT FIND GOOD
RESULTS....
IF THE WINDING IS DAMAGED .... WE WILL GET ZERO VALUES ....
ex: HV SIDE 1U-1V = 1V-1W + 1U-1W
440V = 440 + 0
AND ALSO LV SIDE : 2U-2N = 2V-2N + 2W-2N
90 = 90 + 0
THIS IS THE ACTUAL APPLICATION OF MANGNETICA BALANCE TEST...
THANKS....
| Is This Answer Correct ? | 287 Yes | 9 No |
Post New Answer View All Answers
how many Classification of fire extinguisher
what is JE exam?
What are safety device in vcb and acb?
What will be the output voltage of a transformer if it is primarily energized from a square wave voltage source?
what is relay what is protection & contact multiplying relays where it is used function in brief
how we can explain arc heatng?
What is Surge Capacitor? Why it is use in Generator Circuit Breaker?
what is the voltages using in movie theaters??? why ??why not other??
List of equipments required foe industrial repair lab.
Difference between transition and diffusion capacitance
I am going to appear RRB Sr. Section Engineer Exam, Electrical. Can you send me previous year questions of RRB Electrical engineer. specially Section Engineer questions. my email id is likerahulworld@gmail.com
dear sir, i completed diploma in electrical in 2005, how i can get electrical supervisor liance in mumbai
If more than rated DC voltage appears across trip coil of the breaker, what will happen? e.g. in 110V DC circuit system, if voltage across battery terminal showing 121 V
what is a vector protection in transformer
I PURCHASED A DEISEL GENARATOR SET OF AVR TYPE& RATING 125KVA BUT SOME TIMES THE OUTPUT VOLTAGE IS FLUCTUATING WHAT ARE THE PROBABLE REASONS GIVE ME