How will I know that how many batteries I should connect to
my UPS unit?
Answer Posted / shamim ahmed
You Should Know the KVA rating of your UPS, time you want
to get Back-up & the Battery input voltage of your UPS.If
your UPS rating is X , time T and the UPS input voltage is
V then the Battery current capacity is:
I=X*T*1.25/V*0.7 AHr
suppose battery input voltage of your UPS is 36V and you
find the Battery capacity from calculation is 300Ahr.
then you can use 3pcs 12V 300AHr battery in series or you
can use 2pcs 36V 150AHr battery in parallel.
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
how to calculate the change over time for star delta starter for different KW motor?
what is acceptable leakage current for 33kv cable while doing high voltage test for cable? how to calaulate the leakage current for 33kv or any rated cable?
Trafo ratio is 11kV/6.6kv,Vector group is YND11. What will be the effect if secondary is used for earthed system.
write a program that prints prime numbers from 1-20 in digonal form
In a single how much maximum current and watts using
In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?
IF % IMPEDANCE OF A TRANSFORMER IS INCREASED FROM 5.8% TO 8% HOW MUCH THE EFFICIENCY OF THE TRANSFORMER WILL COME DOWN?
how to select fuse rating for a 3-phase motor ???
what is PWM in IGBT and how it works for drive.?
What is meant by Load Encroachment in OHL Feeder Protection?
How many types of probe used in cro?
what is spadar bar .why I use in DC generator.
Explain the difference between verilog task and verilog function?
An ELHNC 80amp 240v 30mA RCD is tripping periodically, every 30 - 180 seconds is it safe to disconnect the protection circuit?
where lt & ht capacitor used