Why Transformer in KVA?
Answer Posted / pankaj rajput
The copper loss of a Transformer depends on current i.e.
I^2 R and the iron loss depends on voltage. Hence the total
losses depends on volt-ampere (VA) and not on phase angle
between voltage & current.
Therefor the losses in a transformer are independent of
power factor which is cosine of angle between voltage &
current.
That's why the rating of transformers is in KVA and not in
kW.
Now coming to Efficiency of a transformer: Yes it depends
on power factor of load. Because the
Efficiency = Output/Input
= (Input - Losses) / Input
= 1 - (Losses / Input)
= 1 - [Losses / (Vs * Is * Cos phi + Losses)]
Efficiency is inverted V curve (Y-scale) and the peak of
curve appears between 50-60% load (X-scale)for various load
power factors. Efficiency increases as the power factor
increases.
| Is This Answer Correct ? | 23 Yes | 6 No |
Post New Answer View All Answers
WHAT IS THE CURRENT CARRYING CAPACITY OF 2.5/3 CORE HI TUFF CABLE,WILL IT SAFLEY CARRY 8.6 AMPS OVER 120 METRES,CAN YOU ALSO ANSWER WITH FORMULA FOR WORKINGS OUT ,THANK YOU 3RDYR APPRENTICE.
How short circuit MVA(Fault MVA) in a power system calculated for calculating number of earth plates ?
Explain what is clipper and clamper circuits?
What is the difference between Encoder and Resolver?
explain Density
In a synchronous motor. if start is running at high speed. What will be the starting torque : Higher Lower Zero
Keywords: Die, Card, Coin, B/N 2 To 12
Why saturation region slowly shifted in the left side?
What are the properties of a resistor?
can anyone send me some sample question regarding power grid corp
What do you mean by per capita requirement of electrical energy in india
Comment on the working principle of operation of a single-phase transformer.
On what cycle does thermal power plant operate?
What is “pu” in electrical engineering?
What is the difference between the transmission line and distribution line?