HOW TO FIND OUT 1. LINE CURRENT, 2. PHASE CURRENT IN AN
ALTERNATOR / TRANSFORMER WHICH IS FEEDING A I)STAR LOAD ii)
DELTA LOAD, USING A CLAMP METER.
NORMALLY WHEN WE USE CLAMP METER IN A DG SET THEN WHAT DO
WE GET?? PHASE CURRENT OR LINE CURRENT.
Answer Posted / nirav_patel2120
The current flowing in each line is called line current.&
Current in each winding is likewise known as phase current.
In star load
line current=Phase Current.
In Delta load
line current=√3 Phase current.
Is This Answer Correct ? | 2 Yes | 4 No |
Post New Answer View All Answers
What are the differences between single phase and three phase?
Can we use 230VAC, 63A MCB for 120VAC, 63A supplied heaters load?
Minimum IR value of 1.1 kv grade 3.5c (300, 240,185,150,120,95,70,50,35,25) sqmm Aluminium XLPE cable and 4c (16, 10,6 & 4) sqmm cu arm cable between RY,YB,BR,RN,YN,BN,RE,YE,BE & NE.
Why mostly the HV side of transformer has Delta?
why ct ,cvt should be stored in a vertical position?
State the frequency for rc phase shift oscillator?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
excitation limit of an excitor
What is the BS(British Standard)code for 11kv motor
What is the maximum operating temperature for a thermoplastic insulated cable?
why moisture formation found in XLPE Armoured cable outer sheath
How to use computer cpu ups use for home inverter circuit board
WHY L-G FAULT IS MORE SEVERE IN TERMS OF RRRV?
we use capister for power factor. when we use capaciter in dg circuit than defect dg. can we use capaciter bank for dg circuit
whit is 33kv power 300*300 cable full current with formula