What core magnetic balance test of transformer?
How to do this test in a three phase Star delta (star-LV,
Delta-HV) transformer?
How to measure and where to measure?
thanks and regards
Austin
Answer Posted / mugaisi
Provide 2-phase supply on the HV side of transformer on two
phases.
Then measure magnetizing current in the supplied phases.
Then measure the voltages on the LV side.
Repeat the same for the other phases and measure current
and LV corresponding voltages.
The LV voltages should obey
ry = rb+by
and
rn = bn+yn
| Is This Answer Correct ? | 39 Yes | 21 No |
Post New Answer View All Answers
How can maintain our H.T. motors used in cement plant. please send me procedure.
briefly explain the main blocks found in a microprocessor based system
What is the effect on power factor, shown by a trivector meter; incase of reverse phase sequence. If the power factor of a system is lag what meter will show in case of reverse phase sequence connected to the meter. and What in case of lead.
What is Electrical Grade Aluminum for Tubular BusBars. i am confused between 6063 and T6 or T5 and what is BS 2898 and BS 159?
How to size Air Circuit breaker (ACB)? What is the most important factors?
State The Difference Between Generator And Alternator?
Define delay time.
show the single line diagram of star delta starter with single phase preventer
Define demand factor?
explain remenance . differentiate high remenance type ct & low remenance type ct
1. Can a 12v DC choke operate a 60v/12w PL lamp ? 2. Can a 230v ballast fire / operate a 60v/12w PL lamps.
what is the difference between an alternator and a synchronous motor
why we need to us lenz's law for synchornous motor
what is the difference between earth leakage and earth fault?
An active element is one which a. Supplies energy b. Absorbs energy c. Supplies energy and convert energy from one form to another