What core magnetic balance test of transformer?
How to do this test in a three phase Star delta (star-LV,
Delta-HV) transformer?
How to measure and where to measure?
thanks and regards
Austin
Answer Posted / mugaisi
Provide 2-phase supply on the HV side of transformer on two
phases.
Then measure magnetizing current in the supplied phases.
Then measure the voltages on the LV side.
Repeat the same for the other phases and measure current
and LV corresponding voltages.
The LV voltages should obey
ry = rb+by
and
rn = bn+yn
| Is This Answer Correct ? | 39 Yes | 21 No |
Post New Answer View All Answers
why the difference arise between HT reading & LT reading (submeters fixed in complexes, apartments etc)if the power factos exceed from 0.9 to 1 can the ht meter reads fast?
how is the testing of an REF relay? what are the test REF circuit having?
Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!
Define ohm’s law for a.c (alternating current)?
3- What is the target from Zero Impedance, Single Phase Imp., S/C Imp. and magnetic balance tests?
what is the difference between Central Battery System and UPS in applications and uses? and why UPS suitable for Computers and central battery for emergency lighting?
What are the limitations of Kirchoff's laws?
What is the differance between 2 dc motors of armature voltage 660 v and 440 v?
What will be the voltage impact on secondary side of two transformers with different vector groups when both voltages are compared.
is there any role of power factor with frequency variation? and how we can manage the frequency variation?
how you taken aotitude test
What's mean HVF & HAF in Vacuum Circuit Breaker?
what type of motor used to move a 1 ton gate? and relate ratings with load.
What is the difference between electronic regulator and ordinary rheostat regulator for fans?
what is consequences of neutral and earth connect?