Why use the VCB at High Transmission System ? Why can't use
ACB? Pls explain the ans.
Answer Posted / rajesh dhankar
i'm sorry to say that above two answer give above are half
correct. because all u r talking about ionized air if u ever
open Chamber where CT's and PT's are connected u will find
distance less than a hand away and there is no problem of
ionized air there.
The main reason after that is at a time of breaking a ckt or
can say shutting down a ckt when load is not completely zero
there can be big damage or accident because of higher
voltage rather if load is completely zero then there is no
problem.
and ACB are used in low tension line where low voltage and
higher load can be controlled.
Is This Answer Correct ? | 3 Yes | 5 No |
Post New Answer View All Answers
can we use ZNyn11 transformer instead of Dyn11 transformer in distribution for effectively eliminating harmonics from the industrial loads.
In how we connect watt meter for open & short circuit test of a single phase transformer.
In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?
11kV capacitor bank of rating 2.4KVAR, is charged with protective relays of only over current & Earth fault &.......without Over Voltage, Under Voltage & Neutral Displacement Relay. Is it advisable??
what is the purpose of slope in the differential relay?why we are using two slope?but in busbar differential we are using only one slope.why?
please send the IS strandard for electrical to sakthi_murugan86@yahoo.co.in
List out the different frequency domain specifications?
How test for Ddo vector group test condition?
What is VSCF windelectrical system?
Initially, when the input is not equal to the output — what type of response is this?
what are the basic insulation levels & what its Unit
can we use CBCT in neutral of solidly grounded transformer? in place of three phases we can pass only one phase which decreases the size of CBCT?
why tertiary winding is used in transformer with diagram?
what is the VA(Volt-amphere)? define with calculation?
what are the protecyion of transformer & generators