why do we use magnetic contactors ?circuit breakers are not
enough?
Answer Posted / sunthosh080
Usually the mechanical life of the contactors will in
millions times and they are very easy to control and
operate. Other breakers are large in size and difficult to
control when compared. Also the opening & closing time will
be very less for contactors and in case of any short
circuits contactors can be easily repaired.
| Is This Answer Correct ? | 31 Yes | 5 No |
Post New Answer View All Answers
What is the meaning of Insulation H for transformers????
Why the output of OP-AMP is always less than Vcc?
What is the difference between the relay and the circuit breaker?
What is A check, B check, C Check & D check for a diesel Generat
what is the eight bit unit?
i have seen one 8.4 MW synchronous motor in a plant located in bellary it is fixed with brushless rotary rectifier ,anybody can explain its start up principle
How to work E.L.C.B and how to connect in circuit.
how to test YNyn0 vector group in transformer?
How to design a Unit auxiliary transformer for a power house having a unit of 65 MW and Generating voltage of 11 KV and Secondary voltage of 433V
If a high resistance fault occurs,then what are the changes will happen in the system?
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test. why transformer rating in always in KVA ? what ispositive, negative, zero sequence impedence? How ElCB tripping if Neutral touch with ground Why AC & DC capacitor are use in UPS ? why motor rating in KW? how to syncronize two dg sets
how to calculate mf when meter and cTPT detail are given
what is the difference between directional & non directional earth fault with example please explain.
what is efficient motors and how it is different from normal induction motors
I completed my BE EEE degree 2006 .... which license should i apply .... ?????