in slip ring motor if motor specification is given how we
calculate its rotor resistance in starting

Answer Posted / venkat

V, Power rating is given
at start s=1
Nr=(1-s)*Ns
ir=sE2/sqrt of (r2+sE22)
P=sqrt(3)*V*I* Cos pi
from which we get r2

Is This Answer Correct ?    6 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is the drawback of class b amplifier? How is this minimized?

674


WHY NUTRAL GROUND SYSTEM USED IN 33KV SYSTEM

1804


How to Calculate the Fault Level of Electrical Installation

1757


how to calculate insulation level of transformer?

1102


How to calculate total harmonic distortion level(THD) in VFD? and how can we reduce harmonics?

3617






What are the advantages of the three-phase motor over single phase motor?

611


What is conventional thermal current (Ith)

3840


Explain the working of variable frequency transformer?

662


what are the industrail measures to over ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system?

1687


DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.

1444


WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??

1756


What is the function of interposing current transformer?

610


why sielent pole is used only in hydro generators and not in turbo generators

3366


for 100 HP Induction motor service factor is 1.2(SF) we placed a VFD at the motor side load is balance with 0.3 Amp's Phase to Phase but at incoming of VFD load is un-balance with 10 to 20 Amp's what will be cause of load un balance

1529


what is the breaking capacity and making capacity of circuit breaker and how

1597