what will be happen if we apply D.C supply to the
transformer
Answer Posted / shalini
Transformer has two windings primary & Secondary.
When AC supply is applied across primary, due to the
changing current flux will be produced & due to incuction
EMF will be induced in Secondary also.
Whereas in case of DC there is no change in current & no
induced EMF so the Transformer windings will get burnt
| Is This Answer Correct ? | 47 Yes | 4 No |