what will be happen if we apply D.C supply to the
transformer
Answer Posted / shalini
Transformer has two windings primary & Secondary.
When AC supply is applied across primary, due to the
changing current flux will be produced & due to incuction
EMF will be induced in Secondary also.
Whereas in case of DC there is no change in current & no
induced EMF so the Transformer windings will get burnt
Is This Answer Correct ? | 47 Yes | 4 No |
Post New Answer View All Answers
what happend to DC shunt motor if its field winding insulation becomes slightly weak? will that motor can run on full load or not explain in detail. thanks
How cmd is calculated in case of energy neters
plz tell me,ht and lt panel terminals in substations explain beiefly
A 230V dc shunt wound motor has an armature resistance of 0,15Ω.When operating on no load at 650 rev/min the armature current is 6A . The motor takes a full load current of 85A. Calculate the full load speed if the field flux is (i) maintained constant (ii)reduced by 0,03
solar inverters was not connected to the nuteral link .this nutwral possible to any other systems
what is residuel magnetism. and how order lead acid batteries for 24 volt. emergency lighting system.
describe the A.C. Generator Testing procedure
what is the synchronous timer ? and it applications.
What are the classifications of oscillators?
What is difference between isolator and circuit breaker?
The specific heats of the gas at constant pressure and constant volume are respectively 1.0 kJ/kg K and 0.72 kJ/kg K; the value of R for the gas is
Why we use 4-20 mA Analog signal for the PLC input? Why not 0-20 mA? Why not 5-25 mA?
how to calculate power consumption in slip ring motor at different step
What do you mean by reach and reach the point of the relay?
Explain RLC circuit?