What is the function of trip neutral close switch?
Answer Posted / sanket patil
A TNC SWITCH IS ALSO CALLED BREAKER CONTROL SWITCH. IT IS
LOCKABLE IN THE NEUTRAL POSITION AND IS A THREE POLE SWITCH.
WHEN IT IS IN CLOSE POSITION THE COMMAND IS GIVEN TO THE
CLOSING COIL OF THE CKT BREAKER AND THE BREAKER CLOSES.
WHEN IT IS IN THE TRIP POS COMMAND IS GIVEN TO THE TRIP
COIL OF THE CKT BREAKER AND THE BREAKER TRIPS.
| Is This Answer Correct ? | 9 Yes | 7 No |
Post New Answer View All Answers
What are the types of transformers according to the arrangement of iron cores?
mention hazard experienced during installation
Define maximum demand?
What are the different towers used in 132kv transmission line? what are the differences between the P,R,S towers used in 132KV and detailed explanation
What is the function of electron gun assembly used in crt?
what do you mean by type zero control sytem ?Give an practical example of type zero contol sytem?
This is urgent!! What is a Thyristor-based 3-ways selector switch with Zero crossing control? how does it operate and where is it mostly found in a system?
at what rate the micro controller increment its timer....is it 1micro seconds or 1/(12*10^6) seconds
what heppend if we are connected u1-v1-w1 as a star point in the place of u2-v2-w2 in power genration
Is it possible to obtain 480v or 550v in single phase output by giving the input to 230v to a single phase torodial type transformer without using a stepup transformer?
Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?
why i can not use thimble on capacitor duty contactor
Compare jfet’s and mosfet’s.
what will happens if one phase is missing for 33/11kv power transfomer and why?
What are the types of class b amplifier?