How can we calculate the fault level of the distribution
system knowing the percentage impedance of transformer &
subsequent equipments.
Answer Posted / k n naidu
hi,
Calculation of fault level of a distribution net work of
complex in nature manually is laborious. Use network
analyser for simulating the network and fault at the
required bus to get the fault current.
for manual calculation use the MVA method which is
simple and gives fairly acurate results
Is This Answer Correct ? | 23 Yes | 7 No |
Post New Answer View All Answers
Air refrigeration cycle works on the
What is the minimum value of hfe for the oscillations in transistorized rc phase shift oscillator?
what are the stresses in circuit breakers ?
Give some example of fault limiting devices?
I am interested to know what does 15 KVA DG set actually means? If I dont know the DG rating, is it possible to identify KW by simply knowing the diesel consumption?
What is the Basic Difference bitween Long Shunt Connection and Short Shunt Connection in DC Generator?
can someone explain that how the speed of the protection system affects the fault level calculation?
what id a dry type transformers and its function ?
If i have two 3000 kW motors and the whole facility requires a 10 MVA transformer. What would be better installing two 5 MVA transformers(one for 1 motor ) or just a single 10 MVA transformer for both of them. Give reasons for your answer.
what is the difference between 50 hz freq. and 60 hz freq.? which is better and economic in them ?
what is the reason the main breaker is trip during the motor is running? (some time the breaker is not trip)
What is use of starter and choke in tube light
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
how to electronic energy metter failed in electomagnectic fild passing in the metter and which thing to defect more on metter.