How can we calculate the fault level of the distribution
system knowing the percentage impedance of transformer &
subsequent equipments.
Answer Posted / k n naidu
hi,
Calculation of fault level of a distribution net work of
complex in nature manually is laborious. Use network
analyser for simulating the network and fault at the
required bus to get the fault current.
for manual calculation use the MVA method which is
simple and gives fairly acurate results
| Is This Answer Correct ? | 23 Yes | 7 No |
Post New Answer View All Answers
Why it is necessary to isolate fire fighting when you are taking shutdown for lv board.
Whats the minimum value for I.R. that can be allowed for HT & LT alternators for operation?
why magnetising curve not start with zero voltage?
What was your role in the silicon evaluation/product ramp? What tools did you use?
What are the reasons for the parallel operation of transformers?
what is interfacing in computer studies?
please tell me how a surge protector work on a DC 48Volt.? please describe briefly.
I am apply the AAI. So i want electrical sample question paper in technical with answer my id is vijayjobsmart@gmail.com
How to calculate Temp from Resister from PT100 equation,
diff. between tension mode & speed mode
hi,every one, i have to write the search paper on "performance policy optimization" of NGN (next generation networks). i need the material on this topic. can any body help me. please tell me any useful site where the good material is available and name of any reference book. it should be a great help for me.
what is there inside an inverter and how it works?
what is the effect of change in supply frequency on load angle of synchronous motor,all other parameters remaining same?
for 5KW resistive load can anyone please suggest me whether to go for UPS/Inverter or Generator depending upon cost calulations
what are the application of over current relay?