Answer Posted / anshul kumar goyal
According to KCL
Cuurent coming to the point+current going away from the
point=0
Therotically same rule applies in star connection only if
load is balanced, but practically current at neutral point
is not 0 as .
To make the neutral current 0, earthing is provided in the
transformer commissioned at DT through a bush.
This earthing provides minimum resistance path for the
accessive current.
| Is This Answer Correct ? | 9 Yes | 7 No |
Post New Answer View All Answers
For small size, high frequency coils, the most common core material is- a. )Air b. )Ferrite c.) Powdered ion d.) Steel
Is it required to lay 2 runs of GI wires along with armoured cables from one power DB to another Power DB?
if the motor rated speed is 950rpm. how to change the above rated speed? is it possible?
What is the selection process of breakers. Can any one please give a formulation on same?
what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?
can we synchronize star system generators with delta system generators?
what is the meaning of vcc
What Maximam Gap Taibaar & Bush
i have a 4 Mva transformer 34.5 kv / 480-277 v and i used 2 parallel 3200 amp bus duct for the secondary feeder using 3 ply of bus bar ( 3/8" x 5" ) as a common where the flexible link terminated and 6300 amps breaker for the main, the lower bus duct reaches 70 degrees and the upper bus duct reaches 55 degrees when i used thermal scanner. why the temperature is not balance when the load reaches 3600 amps.
how we provide neutral earth on synchronising panel as per electrical standards?
how load of a turbo generator can be increased
I Have 3 Phase 10 KW AC Alternator i found one phase weak, so what will be the reason & what action shouls i take to rectify the same.
Why can't we parallel Voltage transformer secondary circuits?
Why does the rotor rotate?
I HAVE BEEN SELECTED FOR APGENCO A.E(ELECTRICAL) 2008.HOW MUCH WEIGHTAGE FOR INTERVIEW AND WRITTEN TEST.HOW I HAVE TO PREPARE. PLEASE GIVE INFORMATION IF U KNOW.WHAT ABT G.D THIS TIME.CALL RATIO 1:2