Answer Posted / srikrishna kumar
the operation of the relays depended upon the magnitude of
current or power in the protected circuit. however,there is
another group of relays in which the operation is governed
by the ratio of applied voltage to current in the protected
circuit. such relays are called distance or impedance
relays. in an impedance relay, the torque produced by a
current element is opposed by the torque produced by a
voltage element. the relay will operate when the ratio V/I
is less than a predetermined value.
| Is This Answer Correct ? | 13 Yes | 11 No |
Post New Answer View All Answers
what is the function of gss in the dg set.
in 6.6 kv vaccum circuit breaker vaccum bottole vaccum capacity ????
What is the rotor frequency of 10 Hp 1440 RPM 50HZ 415V ?
What is dynamo?How it works and what is the function of dynamo in a DG.
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
how solar power plant energy meter multiplication factor
What is the difference between UPS & inverter ? which UPS is better and whos got the edge ? what is the difference between & inverter ? which UPS is better and whos got the edge 12 V , 24 V , 36 V etc what are the advantages of 12 V, 24 V , 36 V etc and what are the disadvantages of 12 V, 24 V, 36 V etc thanks
what is the meaning of the symbol << >> put in transformer drawing
When a square wave is applied to primary of a transformer then what will be output wave form of secondary ?
what are types of encoder
What is deference between MCB & MCCB & ISOLATOR
if negative of DC supply used and positive is grounded through EGB, and if ELCB used in the system then is it sense the positive volatge and get tripped is it possible?
I need bhel electrical test pattern & paper
Why efficiency in thermal power plant is low?
who can measure the size of power cable?