Answer Posted / sudhir
inrush current is refers to maximum, instantaneous input
current drawn by electrical device when first turned on.
when a T/F is first energized a transient current much
larger than the rated T/F current can flow for several
cycles.this ts caused because the T/F will always have some
residual flux and when T/F is energized the incoming flux
will add to the already existing flux which will cause the
T/F to move in to saturation.
due to this the starting current is double the rated
value. this us not a fault, our protecting system is
designed such a way that it can with stand with this inrush
current without any tripping.
| Is This Answer Correct ? | 32 Yes | 4 No |
Post New Answer View All Answers
Mention how NPN and PNP transistor works?
what is the differencce inn series and cascade connection??
explain why core loss of a transformer is almost constant under different load conditions when connected across a constant voltage and constant frequency.
if a number of plc s are there then how many modbus to be used
What are the necessary components of the feedback control system?
Can 4pole (3 phase+neautral )RCCB proper functioning in only 3 phase load (no neautral, no Earth) ?
How may I enrol or get admission to your program?
Whether amorphous core transformer is commercialized or not:Name of company making amorphous core transformer and what are different rating?
HOW TO CALCULATE HV CABLE SIZING?
how to get electrical supervisor competency certificate in gujarat. i did 3 year diploma in electrical
what is meant by rotating magnetic filed
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
if 3400kw slipring motor rotor shorting done and motor started on mv drive ,what will be the rotor shoring current
what is there inside an inverter and how it works?
how power is generated,and transmitted to our home..pls explain briefly in simple words.