Answer Posted / yogesh
If you run too much current, or too low a frequency, then
the core will saturate. This means as the current
increases, you do not get an increase in magnetic flux.
This is a bad thing, because it means you have no
inductance at that point. So if you apply a ac voltage from
a low impedance driving source to a coil that has very low
inductance, the current will be excessively high!
| Is This Answer Correct ? | 19 Yes | 21 No |
Post New Answer View All Answers
Mention what are the types of semi-conductors?
why 5kW motor becomes unbalance if its relay trip 1st time and its set value is 7.0 A
What is fault clearing time for Current Limiting Moulded Case Circuit Breaker?.
What is Electrical Grade Aluminum for Tubular BusBars. i am confused between 6063 and T6 or T5 and what is BS 2898 and BS 159?
What is FTA card? How it works?
how does the thyistor work in dc drive?
how many single tension hardware are required on a double circuit transmission tower?
What is the role of power pack in substation protection system?
What is the vector group of a transformer,how can it be found out?
how to calculate insulation level of transformer?
what are the precuation should be taken ahen installing power transformer,circuit breaker,current & potential transformer
What happened when voltage will half value of current ...
where we use the SFU & FSU?
What is a signal flow graph?
what is the purpose of using filters in a protective relaying scheme?