WHAT HAPPEN WHEN CT SECONDARY OPEN DURING LOAD

Answer Posted / imran

In normal power transformers primary current depnds upon
the secondary current ( load on secondary side, as load
increases its secondary current increases and also primary
current increases )
While in CT primary current is independent, if CT secondary
opens secondary current becomes zero while primary current
remains as it is. Both currents counter each other during
normal operation, and if secondary opens so secondary
current becomes zero and due to the primary current ( now
no counter effect present ) its core becomes saturated and
CT may blast.

Is This Answer Correct ?    6 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how we calculate torque ? how we improve it ?where torque will either motor or generator ?

1781


Generator,motor and alternator Working principal Please explain easily

1170


How to do bus bar short circuit calculation for 230KV/11kv, 60 MVA Substation?

4446


What is a copper loss or i2r loss pc?

887


What should be the length of transmission line so that we can see/obtain the full sine wave of voltage??

1623






How much ph is maintained of water electrolyte which is used in LRS for 1200 kw slipring induction motor ?

1445


how to calculate

1353


what is the IEC standard for Power Cable installation in onshore (like in direct buried ground or above groung)

2364


Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.

1861


TELL ME WHAT IS INDUCTOR AND CAPACITOR WHAT IS IT BASIC OPERATION ANDFUNCTION?

1755


what is lumped and distributed elements?

1703


how to calculate the magnetizing current of ct ( 800A/1A) for Relay 64

1211


Differentiate between digital phase converter and ordinary phase converter.

953


What is the difference between single point and double point bonding. please kindly detail about bonding of cables.

2133


why the rotor current becomes in steady state during high slip region? please verify with equations.

1735