can u please tell me how VFD(variable frequency) drive is
used as a energy saver....?
Answer Posted / girish kumar samal, hindalco,h
in vfd we change both frequency & voltage. as we control
frequency so speed will control * hence torque &hence
current. as both current , voltage controlled so energy
saved.
| Is This Answer Correct ? | 6 Yes | 7 No |
Post New Answer View All Answers
What are unstable systems?
What is the working principle of servo motor? And explain it.
Pls explan the OLR setting in VCB at HT yard
What is pi controller?
how to select rating of HT Panel
describe the Operation of induction generators from bus bars
What is the technical difference between On delay timer and a Star delta timer?
According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.
raleigh method
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
how much GROUND & NEUTRAL VOLT maintain in data center.
Discuss the effect of sudden loading of an induction motor
at work we have a 3 phase motor but on testing one phase isnt getting a reading. it runs 24 hours a day all week. stops and starts well no noise or heating. the phase isnt down to earth.is it just a bad meter reading or not? phases one and three came up with a resistance reading of 0.4 but phase 2 couldnt get anything shows up as open circuit.
what is effect of 5amp fuse on 2mva pry protection of transformer
if main CT is of ratio 50/5, and meter CT is -/5 what will be overall multiplying factor of meter.PT is 11000/110 .