How do determine the Size of a Droop Current Transfomer for
Paralleling of Two Generators, Say I need a Droop Current
transformer for a 600 kW generator need to be parallel with
a 800 kW generator, etc.
Answer Posted / satish babu
Consider two parameters to descide the CT ratings,
a) Primary current on the phase is 1050 amps,Consider No of
leads it has from the generator - If one cable is connected
your primary can be 1000A-1200A
If two leads are used , use only one lead as CT primary
then the CT primary can be 500-600 A
b) Your secondary can be 3A / 1A / 0.5A depending upon the
AVR used
| Is This Answer Correct ? | 8 Yes | 3 No |
Post New Answer View All Answers
what is meant by directional earth fault and non directional earth fault? describe both.
Whar is the KvA rating of 33Kv substation & actual kv rating of power generaating station.
what r PID controllers?why they r used?what is there purpose?plz Explain in detail
how to measure the current by compact digital equipment with dislay which fit inside any equipment
what may the reason for vector shift in a generator?
what type of earthing do for dry fissure rock?
please send the last 5 years {{{JUNIOR ENGINEER - ELECTICAL, ELECTRONICS RRB CHENNAI and secundrabad}}} TECHNICAL question papers TO MY EMAIL ID dinesh100701@gmail.com
sir please tel me how calucalte kwh if home taken load 30ams how maney kwh taken per day.and 3phase motor 5hp per hars how maney load teken and how mach kwh and forward me to electrical table for calicalte kwh and kvr and kvah
should %impedance be high or low in a power transformer? if so why?
In what condition the HT fuse breakes?
why capacitance effect is predominant in underground cable transmission and inductance effect is predominant in over head line transmission?
Alternator rotor earth fault relay circuit
what is the IEC standard for Power Cable installation in onshore (like in direct buried ground or above groung)
what are different types of electrical windings? i know the distributed winding ,concentrated winding etc but i want some detailed information, in what condition we will use distributed,concentrated windings what are the difference between them which is best, how induced emf changes by using different types of windings 20 hours ago - 1 week left to answer
what is meant by loss of field in a DC motor? how a universal motor works?