Answer Posted / kalirajan.n
system, a prime mover drives a direct current (DC) generator
at a constant speed. The armature of the DC generator is
connected directly to the armature of a DC motor. The DC
motor drives the load equipment at an adjustable speed. The
motor speed is adjusted by adjusting the output voltage of
the generator using a rheostat to adjust the excitation
current in the field winding. The motor field current is
usually not adjusted, but the motor field is sometimes
reduced to increase the speed above the base speed. The
prime mover is usually an alternating current (AC) motor,
but a DC motor or an engine might be used instead. To
provide the DC field excitation power supply, Ward Leonard
systems usually include an exciter generator that is driven
by the prime mover.[3][
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
If we use 250A MCCB as a incomer in Control panel for a fault level of 50kA for one second ,assuming temperature rise from 85 Deg. to 100 Deg , Then what will be the Aluminium Bus-bar size for 250A MCCB? Explain in detail.
WHAT IS DEGREE OF COMPOUNDING IN D.C MACHINE MEANS? HOW TO READ THE OPERATING CHART FOR ANY ELECTRICAL MACHINES?
As we know induction squirrel cage motor torque Directly praprortinal to applied voltage in star connection & delta also. If I connect 55KW Motor to DOL starter in load condition does motor withstand the load & what will be the current withdrawn ? motor will not fail ?
Is RTCC panel needs any control supply.
10 tube light connect in mcb breaker.one tube light is fault.so breaker is tribe.how fault is rectified.(using 3wire phase,earth,neutral)
3phase motor can be used as a Prime mover for alternator.
What are the types of instrument transformer?
(1)Can earth and be conected together (2) what is the diferent between earth & neutral
how the speed of the gets motor regulated. does it draw the same current on the all speed level.
what are the application of over current relay?
In DC generator, we use commutator, having no. of segments. Then how it is possible to get a half wave of voltage and current for half rotation of armature?
I'm looking for a softcopy manual set for a Credence ASL- 3000. Anyone know where I can get it?
how to calculate voltage drop and followed by cable calculation?is there avail in formula?
PLZ EXPLAIN CORONA,SKIN,BIRD PALE,SPAN,SAG Effects of power cable.
How to see the inductance in a transmission lines