WHAT HAPPEN WHEN CT SECONDARY OPEN DURING LOAD
Answer Posted / javed
CT means current transformer which help us to measure the
large amount of current by step down the value of current
to low value. CT primary wdg handle the large amount of
current due to which large amount of heat is produce at
primary winding so we use insulating oil which help to
provide insulation as well as provide cooling. If we open
its secondary winding, the secondary current will reduce to
zero, which cause increase in voltage across its secondary
open terminal and that leads to increase in primary
current, with increase in primary current temperature of
oil in CT also increase and oil start burn which leads to
blast in CT
| Is This Answer Correct ? | 33 Yes | 6 No |
Post New Answer View All Answers
please describe the Transformer setting, Motor setting, I/C setting, Tie setting
what are the condition that makes hooter blow?
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
What is the selection process of breakers. Can any one please give a formulation on same?
why i can not use thimble on capacitor duty contactor
Difference between ac parallel circuit and ac series circuit?
Define steady state error.
whatare the disadvantages occur,if the form factor of transmission will not be equal to 1.11
Why is better to have a minimum ceiling voltage of 250% than 160%?
what do you mean by every IC 74 first digit.why are you using this no.why not using another no.
What is different type of Electrical curve and how it protects the equipment's while up-normal situation?
Difference between control junction box (cjb) and power junction box(pjb)?
Motor,transformers,capacitor tubelight etc....
for 5KW resistive load can anyone please suggest me whether to go for UPS/Inverter or Generator depending upon cost calulations
what is sevice settings for mccb?How can be it setted?