Answers were Sorted based on User's Feedback



How can we calculate the fault level of the distribution system knowing the percentage impedance o..

Answer / kaustubh

if we known the pesentage of impedance then by using this
formula we can calculate the fault Lavel.

fault lavel in MVA= Rated KVa/% of Impedence

OR

Fault Lavel= 1.732xFault Currentx Rated Voltage

Is This Answer Correct ?    146 Yes 38 No

How can we calculate the fault level of the distribution system knowing the percentage impedance o..

Answer / gopal

fault lavel in MVA= Rated power/% of impedence


or

Fault Lavel= 1.732xFault currentxRated Secondry Voltage

Is This Answer Correct ?    69 Yes 28 No

How can we calculate the fault level of the distribution system knowing the percentage impedance o..

Answer / mukul

Dear friends above answer is wrong when you are using
transformer KVA in you calculations then pf is not required
the above answer can be corrected by omitting pf from this calcs

Is This Answer Correct ?    44 Yes 5 No

How can we calculate the fault level of the distribution system knowing the percentage impedance o..

Answer / amar singh.

fault level depend on system impedance
full load current*100
Trasformer fault level= ----------------------------
%impedance of the transformer

Is This Answer Correct ?    51 Yes 17 No

How can we calculate the fault level of the distribution system knowing the percentage impedance o..

Answer / pankaj

THERE IS A SIMPLE CALCULATION IF ASSUMING INFINITE SOURCE
BUS THE MAX LEVEL OF FAULT AT LT SIDE OF A 11/0.433 5%
1000KVA TRANSFORMER CAN BE CALCULATED AS:

KVA*100/SQRT3*433*Z% kAMPS

1000*100/1.732*433*5 = 26.7kAMS

Is This Answer Correct ?    39 Yes 7 No

How can we calculate the fault level of the distribution system knowing the percentage impedance o..

Answer / k n naidu

hi,
Calculation of fault level of a distribution net work of
complex in nature manually is laborious. Use network
analyser for simulating the network and fault at the
required bus to get the fault current.
for manual calculation use the MVA method which is
simple and gives fairly acurate results

Is This Answer Correct ?    23 Yes 7 No

How can we calculate the fault level of the distribution system knowing the percentage impedance o..

Answer / leonard

Fault level = Rated Voltage / system impedence (up to that
point)

transformer impedance can be calculated using the
following formula:

Z(transformer)=(Vsq*Z%)/(P*100)

where
Ztransformer is the source transformer impedance, in ohms;
P is the power of the transformer, in volt amperes;
Z% is the rated short-circuit impedance voltage of the
transformer, expressed as a percentage.

Is This Answer Correct ?    7 Yes 4 No

How can we calculate the fault level of the distribution system knowing the percentage impedance o..

Answer / abhi

Fault level = (Rated power of transformer*100)/(percentage
impedance of transformer + imp of subsequent equipments)

Is This Answer Correct ?    5 Yes 3 No

How can we calculate the fault level of the distribution system knowing the percentage impedance o..

Answer / jojo

rated capacity of transformer divide by its transformer
impedance.

Is This Answer Correct ?    2 Yes 1 No

How can we calculate the fault level of the distribution system knowing the percentage impedance o..

Answer / avatar

When deciding the fault levels, isnt there a time component
as well? I have seen the fault levels being designated
as "350 MVA @ 1 sec". What does this mean? Please help.

Is This Answer Correct ?    3 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

What is the method & formula of Fault level calculation in power Transformesr.

3 Answers  


What is primary and backup protection?

0 Answers  


Which type of transformer used in lighting load?

2 Answers   IMFA,


Why voltmeter is not connected in seris & ammeter connected in parallel ?

5 Answers  


Explain why inductance of the iron cored coil changes with current?

2 Answers  


Is it legal of using 3 phase motors in 2 phase in Tamilnadu?

2 Answers  


what is resticted earth fault protection ? how did it protect & work in power transformer

3 Answers  


Why derating factor os applied on Cables?

0 Answers  


how to crack cgpsc,which type of knowledge it is required,where i can get systematic study material and some tips?

1 Answers  


what is bushing in transfermor

7 Answers   Bokaro Steel, Visa Steel,


wht is the purpose of the earth electrode other then earthing

1 Answers  


how to calulate transformer secodary fault A?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)