How can we calculate the fault level of the distribution
system knowing the percentage impedance of transformer &
subsequent equipments.

Answer Posted / pankaj

THERE IS A SIMPLE CALCULATION IF ASSUMING INFINITE SOURCE
BUS THE MAX LEVEL OF FAULT AT LT SIDE OF A 11/0.433 5%
1000KVA TRANSFORMER CAN BE CALCULATED AS:

KVA*100/SQRT3*433*Z% kAMPS

1000*100/1.732*433*5 = 26.7kAMS

Is This Answer Correct ?    39 Yes 7 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Why an ac systems are preferred over dc systems?

827


What happens if the series current double?

1186


How much pf maintan in dg set in 6o% load,when Dg runnig Neutaal Earthing removed what happen.

1750


size of condotory fron voltage level

1928


How do you calculate the actual power consumption of an inductive load appliance. Say, a deep freezer of 200watts

1852


i have some screw comprressor with 630kw power,i have established them with simple star to delta circuit,by the way there is so much inertia when the screw comprressors start, can you offer me contactors power with 400vac or any cataluge to choose the contactors

1609


th how could we differentiate between armoured copper and armoured aluminium cable what is the basic application? why we prefer the armoured copper as compared to armoured aluminium.

1690


How we select the vector group of 3phase power transformer?

2279


why do we measure VIBRATION in -24vdc and why we adjust gap voltage -9vdc to 10-vdc? i am trying to get this information since 5 years, yet i haven't get reliable answer, i hope i can get from you.

1602


all details of DG UPS HVAC

1747


How to run a three phase motor into single phase........

1753


why is using sensor?what is differece between photoelectric and proxmitty?

1729


12.5 tons a/c is their how much kva generator can recommend to the customer.

1755


hello! sir i did three year of diploma in electrical (2007- 2010) and now i m a student of electrical engineering. sir can i apply for germany visa for study and part tome work over there?

1613


what does a string of resistors in a series will do?