How to calculate busbar size & what is the procedure we
make for determine that?
Answers were Sorted based on User's Feedback
Answer / sujata wagh
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
Is This Answer Correct ? | 246 Yes | 46 No |
Answer / ashraf majid
The busbar size will be determined by the total loads
connected to the bus.This will require a comprehensive
study of nature of loads plus the surroundings of place.
The general procedure will be such that the operating
parameters don't voilate the maximum safety limits of the
bus.
Is This Answer Correct ? | 145 Yes | 65 No |
Answer / kajajohn
to calculate bus bar size normally for copper 1 sqmm =1.3 A
for aluminium 1 sqmm =0.8 Amps
Is This Answer Correct ? | 129 Yes | 49 No |
Answer / bhavin shah
busbar sizes can not be calculated only from overall size.
there are various derating factors like arrangment of
busbar, nos of busbar, spacing, enclouser size, ventilation
in room, temp rise, skin effect, proximity effect etc.
which need to be consider while designing the busbar.
Is This Answer Correct ? | 64 Yes | 15 No |
Answer / akmal
i want to add in vijay answer that the qulity of copper also
depend on amper rating of coper bar
Is This Answer Correct ? | 65 Yes | 22 No |
Answer / jaydev jena
current density= .8 amp/sqmm.that does mean 1sqmm can carry
0.8 amp current .if sisze of busbar is 100mmx 10 mm then it
can carry 800 amp.
Is This Answer Correct ? | 61 Yes | 25 No |
Answer / nikhan
The bus bar size normally for copper 1sqmm=1.3Am and
aluminium is 1sqmm=0.8Amp
Is This Answer Correct ? | 53 Yes | 20 No |
Answer / waves
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
Is This Answer Correct ? | 40 Yes | 7 No |
can you give any example at any parameters?
Is This Answer Correct ? | 62 Yes | 37 No |
Answer / md.mahmudul hasan
we need to consider short ckt(KA) also. Say short ckt level
is 20KA then we need to select busbar accordingly.
Is This Answer Correct ? | 30 Yes | 5 No |
whycircuit breaker is not connected at the generator end where the capacity of the generator is more say 60MW, 100MW etc.
How to find the maximum load, that can be supplied by a transformer.....
iam working in power plant. In hot places tube lights are glowing at the end portion only. what is the reason for that?
If we are given a 10 amp cable type and asked to calculate the number of cores used and the thickness of the cable, how do we do it?? please help...urgent!! i hope the question is clear enough!!
What is application of MCB & How it works
WHAT IS REMOTE CONTROLLED DG? WHAT IS DIFFERENCE BETWEEN REMOTE CONTROLLED DG & NORMAL DG SETS
what is relay
why we use 20 KV, 10KA LA on 22 KV Line
does the power factor of an induction motor improve upon used in parallel with a synchronous condenser , used commonly to provide a leading kva ?
whati s the sludge current in ups
what will happen if the connections of protection ct reverse? will it burn the ct?
In what condition the HT fuse breakes?