How to calculate busbar size & what is the procedure we
make for determine that?
Answers were Sorted based on User's Feedback
Answer / shilesh kumar
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
Is This Answer Correct ? | 0 Yes | 1 No |
Depending on the maximum load current the busbar size will
be determined. Usually for copper it is taken as 2 to 4 Amps
per square mm and for alluminium it is taken as 1 to 2 Amps
per sqmm.
The normal availability and design of the busbars is
25*5mm,50*5mm,50*10mm,60*10mm.
Is This Answer Correct ? | 57 Yes | 61 No |
Answer / john philip
As per the load we have to calculat but we should choos a
good conducter with low resistenc value
Is This Answer Correct ? | 11 Yes | 16 No |
Answer / hasan 325
to calculate bus bar u must follow this formula :
wiedth x thickness x1.6 A
And also u can use this information :
A/mm2
100A = 2.5mm2
100-500 A=1.75mm2
500-1000A=1.2mm2
1000-above=1.1mm2
Is This Answer Correct ? | 40 Yes | 80 No |
what convarts RRA in alternator ,AC to DC or DC to AC,
I have a small system with two motors that are running on 380 vac, 60 hz. These motors are expensive and I usally get them from Brazil. I am adding another motor to the system, but I want to purchase a 480 vac, 60 hz motor to use. It will be on a VFD that is rated fro 380 thru 480. Is this posible and will I have to use a larger motor and derate it?
0 Answers US Electrofused Minerals,
WTA used cb?
dear all i am kumara now current working in electrical designing of control and relay panel i want learn some substaion design then any book are available. pls mention name and authour
How can we calculate D.C.Load current in terms of A.C. load current?
can i know how to design overcurrent setting and earth fault for 11kv & o.433kv system assuming tx 1000kva.
PIU how does work?
1 no. 22 kV feeder is taken from state electricity board. 350 MVA is the S.C. MVA. now i am feeding this feeder to HT Panel having 2 outgoings which further supply to 2 Transformers. Can you please suggest me the type & rating of cables are 3 of these cables same? or they are different? please help...............
What happens with squirrel induction machines if the ends of rotor conductors are kept open? Explain
how to ctrl motor by use of ac or dc drive.plz explain evdintly
how actually an anti pumping device works? what is the operational principal?
what is the difference between droop mode and ischnorous mode in thermal powerplant?