Is your generator is automated or manual if so do you know
the circuits?
Answers were Sorted based on User's Feedback
Answer / yuvi
Honestly, this question does not make any sense. However, I
will try to answer to the best of my understanding.
1) I don’t have a generator.
2) Difference between manual and automated generator is
that in a manual start generator, we will have to manually
start it. In an automatic start generator, a circuit senses
that the power has failed and starts the generator
automatically using a small battery powered motor similar
to the ones that start your car. The sensing circuit can be
of a wide variety. It can be a magnetic relay or an
electronic circuit depending on the area of application.
Is This Answer Correct ? | 14 Yes | 1 No |
Answer / tapas
in both Auto and Manual cases circuit diagram can be found in the Drawing of Sync panel/AMF panel. Its a selector switch by which user can select either Auto mode or Manual mode.
DG start and stop circuit has two ways to operate which can be found on drawing.
1.Manual Mode: In this mode push button start and push button stop operates DG. i.e. when power fails DG can't be started Automatically. Operator should start the DG manually.
2. Automode: PLC senses absence of Power and commands DG to start.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / ferozuddin
generator wiil be function as a manual and also auto .
manual in case of when there will be no interface with the
auto transfer switch (ATS).when generator is interface with
the ATS it will work auto in case of emergency
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mani0786
mannully start genset start manually & wwhen it come with a amf or ats panel it said auto genset well sir your question is out my mind but so i give it a simple sot
Is This Answer Correct ? | 1 Yes | 0 No |
we have 3 types
1.manual
2..auto.3.semi manual
Is This Answer Correct ? | 0 Yes | 0 No |
Its very simple
Take an 230v auxillary contactor with 1NO POINT and 1NC POINT
One single phase connect at one side NO POINT and other end connect to contactor A1(NO VOLT COIL).A2NEUTRAL directly connected.
Positive (+) supply24 v connected at NC POINT one side and other end connected at generator starting switch .
When EB powersupply is there the contactor is on.
When EB supply cut through NC POINT the positive supply passing to the switch so the generator is on.
Its very cheap.
Is This Answer Correct ? | 0 Yes | 1 No |
how to calculate 'In'in a system?
Dear Sir / Madam, Actually we requied 64 A MCB, But i have 32 A MCB = 2 No's this two i have to make series connection and we usw any place? isit possible or not......
4 Answers Hindustan Unilever Limited,
How can we estimate Gen rotor current?
How to calculate or testing the KW in generator
Which type of moter is used in trains, what is the ratting of supply used explain Working principal?
what is formula for zero phase sequence of nuetal earthing transformer of 6.6 kv
Why cannot we insulate HT over head cable to avoid ionization of air around the HT Cable?..By this we can minimise corona loss also..
if 6 earth pit value is 1.5 ohm then what should be the number of earth pit to make the value .8 ohm
Explain RLC circuit?
how to calc. current for 5MVAR,50hz,33kv
Why the underground cables will Punchar? or what is the reason to burst the underground cables?
how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula