Is your generator is automated or manual if so do you know
the circuits?

Answer Posted / yuvi

Honestly, this question does not make any sense. However, I
will try to answer to the best of my understanding.

1) I don’t have a generator.
2) Difference between manual and automated generator is
that in a manual start generator, we will have to manually
start it. In an automatic start generator, a circuit senses
that the power has failed and starts the generator
automatically using a small battery powered motor similar
to the ones that start your car. The sensing circuit can be
of a wide variety. It can be a magnetic relay or an
electronic circuit depending on the area of application.

Is This Answer Correct ?    14 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How to select a cable size for particular load?

1337


(1)The demand for electricity , the amount of renewable generation available, the amount of fossil fuel generation available and the cost of the fossil fuel generation are shown in table below period(hrs) demand(MW) renewable (MW) fossil- fuel(MW) cost of fossil fuel(MW) 00.00 - 01.00 2000 1800 2000 30 01.00 - 02.00 2300 2500 2000 30 02.00 - 03.00 2500 2700 2100 45 03.00 - 04.00 2900 3100 2100 50 04.00 - 05.00 2700 2600 2500 45 05.00 - 06.00 2400 2000 2700 50 06.00 - 07.00 2200 1800 2000 36 07.00 - 08.00 2100 1600 2000 36 Assuming that the renewable generation incurs zero cost, determine an optimal generation schedule(specifying the amount of renewable generation and fossil fuel generation used in each period, the cost for each period and the overall cost for 8 hours.)

1423


ELECTRICAL ENGINEER TEST IN FEWA ANY ONE HAVE KNOWLEDGE ABOUT THIS?????????

565


Is there chopping current in resistive circuit

1546


How can calculate the earthing strip of Copper/GI for rating of 30kV,discharge current 10KA Lightning arrester.

1875






How RTCC panel is working and give single line diagram for RTCC with transformer?

2650


1) why a dg set shows variation of power factor and load when synchronised with other dgs? 2)Why the load sharing is not become equal in all dgs?. 3)When a dg set will not run on auto start?

1541


What is the permissable nutral current of three phase system as per IS standards?

1533


What is the Difference between Ac Drives and Dc Drives? According to application, speed, Torque, cost, Reliability, Construction, Motor etc... Thankyou !!!

1676


We have 250 KW x 2 motors, which are load from 25% to 100% varying load in every minute , so how can we compansate the power factor. pl give your opinions on the above subject.

1423


Explain in details how you would react to an unexpected incident when your supervisor or manager is not around to give instructions?

7319


What is the Good Earth resistance value of G.I & Cu. Chemical Earthing & Normal Pipe Earthing?

1879


What is the feedback in the control system?

632


WHAT IS MEANT BY DERATING OF THYRISTOR?

2473


What is the simplest formula to calculate the rotor diameter of a synchronous generator?

1914