Difference between directional earth fault and
non-directional earth fault
Answers were Sorted based on User's Feedback
Answer / manesh s
Directional Earth Fault is the Fault(between Phase/s to
Earth)in the system,if system is using only one source, so
Fault would be in one direction(towards the system)
where as Non-Directional Earth Fault is the
Fault(between Phase/s to Earth)in the system,if system is
using two or more source, so Fault would be in two
direction(away or towards)
Is This Answer Correct ? | 9 Yes | 4 No |
Answer / jerry smith
Directional Earth Fault detection is used to isolate a
fault, when using more than one source of power input.
Current Transformers are used to verify the net sum of
current as zero between any two sources of power. If there
is a fault, the breaker between the power sources is
OPENED. The protection logic will then see if the fault has
cleared. If the fault has cleared, the fault is on the side
with ungrounded power source, and will protection logic
will trip the ungrounded power supply. Conversely if the
fault continues to flow after the bus tie is OPEN, then the
fault is on the side of the grounded power supply, and the
grounded power supply will be tripped.
Non-directional Earth Fault would be a simple fault
detection, as located on a generator neutral.
Is This Answer Correct ? | 2 Yes | 4 No |
Why high pressure turbines are single flow
transformer shut down process.
whats plant?
what is the trip circuit supervision in an electrical meaning?
Qatar Fertiliser Company (QAFCO) Shortlisted me for interview (got the intel from my source) for Field Operator- Utilities post. Please let me know what kind of questions they asked? ... this position requires 5 years of experience in Power Plant and background Diploma in Electrical/ Mech. ... my Background is Electrical and I am a sub Assistant Engineer (Operation) at a private HFO based Power plant... PS: Please Let me know what preparation should I take to obtain the Interview which will be take place In Bangladesh soon
1 TPH how many Megawatt ?
What is critical speed of turbine
whatis means of PPA & FSA OR SFA in power plant operation
Calculating Seawater consumption for SWFGD system
Difference between electrical and electronics?
If a pump has "N" no .of conections in the discharge. If a connection has a heavy leakage. Then it's motor current get affected or not??
why prds line tapping taken from ms line as Pri SH O/L temp & pressure is sufficient to full fill our requirement of PRDS..