In a thermal power plant ID Fans running with full load but
boiler load is only 80 % give reason ?
Answers were Sorted based on User's Feedback
Answer / lalitshukla
there are many reason for that.
1. furnace or any duct of flue gas leakage.
2.deposition on super heater which clog the passage of flue gas
3.density of fuel below required density of boiler fuel
Is This Answer Correct ? | 22 Yes | 2 No |
There will be soot deposits on outer surface of boiler tube
Is This Answer Correct ? | 17 Yes | 6 No |
Answer / mohamed elnakib
it is due to the air preheater being clogged increasing the
load of the ID fans due to the bad suction and this clogging
is mostly due to the baskets being melted due to the
formation of the ACIDS from the exhaust gases and the dew
point effect .
this is the only logical reason for why the ID fan is 100%
loaded while the boiler is not .
Is This Answer Correct ? | 12 Yes | 2 No |
May be...
1.APH tube leakage
2.Boiler ducting leakage
Is This Answer Correct ? | 11 Yes | 2 No |
Answer / y v subba rao
If the moisture content in fuel is more than designed fuel, id fans has to run at full rpm to sent out the additional water vapor produced from the additional moisture. In fact total flue gas quantity was increased
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ns satyaraj
Provided Id inlet damper is fully opened main reasons are
1 more gases are being handled . Happens when due to infiltration of external air into ducting thru leakages
Fluegas path are clogged at some place, such as at APH, superheater, economiser
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a k handa
Coal feeding may not be as per the required load.
Is This Answer Correct ? | 7 Yes | 8 No |
Answer / alan
the IDF inlet damper may be stocked to fully open.
Is This Answer Correct ? | 2 Yes | 3 No |
why airtel use + 24 volts and other operators use -48 volt
0 Answers ABC, Airtel, INDUS, Reliance,
What vibration parameters are monitored in a directly coupled single cylinder turbine and generator?
Difference between directional earth fault and non-directional earth fault
By any way can we increase the B check hours from 300 to 500
what is actual CAL MODE & cal means?
why expansion bellow is provided in between hopper and vessel in ash handling plant?
what's the moog valve
During shutdown of Steam Turbine,How do we cross the critical speed?
what is the perfect location for furnace draft transmitter in AFBC boiler?
Why we need to maintain furnace and secondary air dp.if it increase or decrease what happens.
why not maintain Ph 7.0 in Boiler because 7 Ph is not acidic and not basic.
Need of oxygen dosing in super critical powerplants?