WHY THE SYNCHRORONOUS MOTOR IS NOT SELF STARTING, AND WHY
THE STATOR AND ROTOR IS COUPLED?
Answers were Sorted based on User's Feedback
Answer / guest
when 3ph wdg is supplied with 3ph supply, a magnetic flux of
const magnetic field rotating at syn speed is produced at
stator.
at first half cycle(a period of 10 ms)N pole of rotor and N
pole of stator are repelled each other as well as S pole of
rotor and S pole of stator.in the next half cycle(a period
of 10 ms)poles of stator interchanged ie., N pole of rotor
and S pole of stator are attracted each other as well as S
pole of rotor and N pole of stator.
due to continuous and rapid rotation of stator poles, the
rotor is subjected to a torque which rapidly reversing.
because of its large inertia rotor cannot respond to such
reversing torque results remains stationary.hence
SYNCHRORONOUS MOTOR IS NOT SELF STARTING
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / baikunth
synchronous motor can run at synchronous speed or not. to
run the motor the rotor has to run at synchronous speed at
starting.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / keerthirraj
synchronsous motor should be heavy load current capacity ,so synchronous motor not self start........to reduce the loss
| Is This Answer Correct ? | 3 Yes | 17 No |
can we use metering current transformer as protection current transformer if not why? & if yes why?
what happen "when Dyn11 is parallel operation with Dyn1"?
While testing the value of the resistance for the earthing rod, two auxillary rods are connected to the earthing tester.What is the working function of a earth tester?
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
how to calculate the magnetizing current of ct ( 800A/1A) for Relay 64
why voltage ratings of xmission are in 11, 33,66kv and why not 11.5 ,16,19 or any other
What is the difference between a verilog task and verilog function?
Why we should not parallel the with EB
stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate
which theorem is used to analyse fault a)thevinin b)Norton c)Superposition d)jordan
how a flip flop can be used as a latch?
Explain working of servo controlled voltage stabilizer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)