what happen "when Dyn11 is parallel operation with Dyn1"?
Answers were Sorted based on User's Feedback
Answer / akhilesh singh
Due to 60deg phasor diff., PD of two secondaries will
arise. Therefor a circulating current between these two
secondary flows which causes shortcircuiting.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dubai
I agree with murali.
Transformer having -30˚ angle (here DYn 11) can be
paralleled with +30˚ (here DYn 1) angle by reversing the
phase sequence of both primary & secondary terminals of one
of the transformers eliminating phase angle errors.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / thatharao
Both the terminals will reverse and Phase displacement will
be zero.So phase angle will be zero.
| Is This Answer Correct ? | 1 Yes | 0 No |
here phase difference between to secondaries will be 60deg
transformers belonging to dy1 could be operated in parallel
with those of dy11 or viceversa by transposing two of
external high voltage connections of one of the
transformers and also corresponding low voltage external
connections .it is not necessary to change any internal
connections
| Is This Answer Correct ? | 9 Yes | 13 No |
Answer / ramniveth and subuhani
same pottential of two neutral cannot be earthed .because
it give rise to third harmonics.so it cannot be paralleled
| Is This Answer Correct ? | 7 Yes | 11 No |
What is Avg. Power Consumption of 2 TR Split A/C???How v can calc. this???
why transformer rated in KVA not in KW ? we know that W= v*i
What is voltage in two phase?
can anyone tell me the website for star-delta control diagram?
how to calculate the settings for shaft ct protn in hydro generators
if transformer core is made of copper instead of steel which losses will increase..please explain
what is the transformer
what is meant by oil filled power & distrubution transformer ? if anybody know the link of detail about above transformers means plz send it i have interview on this week ? plz help me
while we select CT, why the CT ratio is divided by 5?? ex:250/5,15VA,CLASS-1 CT.Why it is divided by 5??Help me please
why maintain the Dg PF is 0.8? Explain?
static chagre
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)