what happen "when Dyn11 is parallel operation with Dyn1"?
Answers were Sorted based on User's Feedback
Answer / akhilesh singh
Due to 60deg phasor diff., PD of two secondaries will
arise. Therefor a circulating current between these two
secondary flows which causes shortcircuiting.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dubai
I agree with murali.
Transformer having -30˚ angle (here DYn 11) can be
paralleled with +30˚ (here DYn 1) angle by reversing the
phase sequence of both primary & secondary terminals of one
of the transformers eliminating phase angle errors.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / thatharao
Both the terminals will reverse and Phase displacement will
be zero.So phase angle will be zero.
Is This Answer Correct ? | 1 Yes | 0 No |
here phase difference between to secondaries will be 60deg
transformers belonging to dy1 could be operated in parallel
with those of dy11 or viceversa by transposing two of
external high voltage connections of one of the
transformers and also corresponding low voltage external
connections .it is not necessary to change any internal
connections
Is This Answer Correct ? | 9 Yes | 13 No |
Answer / ramniveth and subuhani
same pottential of two neutral cannot be earthed .because
it give rise to third harmonics.so it cannot be paralleled
Is This Answer Correct ? | 7 Yes | 11 No |
trasnfarmaer core make
List few applications of d.c series motor?
Stator of 3-phase IM has 3 slots per pole per phase, calculate number of stator pole pairs. A 1 B 6 C 2 D 3
Which UPS (inverter) is better and why ? 12 V inverter and 24 V (two 12 V batteries in series) inverter which is better ......... which has the longer backup which has the greater charging time which has the greater discharging time thank you
What is power factor?
how can we select the rating of Load break switch that is connected to the primary protection of 200 kva 11kv/415v distribution transformer?? step by step calculated answr pls...thnk.u
The Frequency is measured by _________ bridge ?
what is meant by PU value ? anyone can you explain briefly to me ?
What is voltage
why would the rotor rotate at sub synchronous speed against the direction of rotating flux when d rotor of 3 phase IM is connected to 3 phase balanced supply and the stator windings are shortcircuited ??
While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply?
AMF (auto mains failure) control for DG sets at home.