can we use metering current transformer as protection
current transformer if not why? & if yes why?
Answers were Sorted based on User's Feedback
Answer / arun
Selection of CT for protection is majorly depends on the
burden limit and Kneepoint voltage at which the core of the
CT gets saturated,after which it cannot produce the
tripping emf in its core.
So check the burden of CT and kneepoint voltage.
| Is This Answer Correct ? | 19 Yes | 2 No |
Answer / felixraj
the only diff is the knee point voltage
in metering CT this value is very low, because of this
during fault condition the ct get saturated and o/p almost zero
(metering equipments are protected from fault surge)
protection miss leads in metering CT (it may fails or
nuisance tripping)
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / mohammad
Metering and protection CTs have different accurecy class
level as metering CT has 1 class level and for protection
itis represented by 5P,10P etc..
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / mohsen khoshsefat
Introduction to Protection Transformers
Protective Current Transformers are designed to measure the
actual currents in power systems and to produce
proportional currents in their secondary windings which are
isolated from the main power circuit. These replica
currents are used as inputs to protective relays which will
automatically isolate part of a power circuit In the event
of an abnormal or fault condition therein, yet permit other
parts of the plant to continue in operation.
| Is This Answer Correct ? | 1 Yes | 0 No |
What does quality factor depend on in resonance?
what is tower earthing and what for it is required
in thermal power plants by opening the turbine governor valve increase the generator load. how
What is the unit of magnetic flux density?
What is the major difference between cnc and plc. why cant we use plc instead of cnc
how ELCB drip when earth and phase touch together?
If a rotary UPS is in line through grid power; What would be the impact on Power Factor if the load through rotary ups is 25% , 50% , 75% & 100%. Will the power factor reduce with less load?
When both contractor star & delta is hold in star delta motor ?? So what happen in this case ??
Is there any Institution for giving M-tech in Electrical engineering for those who r in service? Give the details please.
how to select proper cable for ct wiring so that drop within the limit.
How to confirm the Phase shifting Transformer VECTOR GROUP relation , as below ZNy11.45d10.45-ZNYy0.15d11.15
Why the power factor of the alternator in power plant is kept .8 lagging. Can't we maintain it at 1.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)