i have 80cm water tank.how can i use DPT as level
mesurment.pls give specs for that..?
We have air comp.from that moisture comeout to one tank.i
want to mesure level of water in that tank and then after
operat one sov to dicharge water after high level.
TAKE TWO TAPINGS, ONE AT 5CM (HP SIDE)ONE AT 75 CM (LP
SIDE). NOW CONNECT THE DPT AS PER HP AND LP CONNECTION AND
IN Tx. ALSO DEFINED THE LSV AND USV IN Tx. IT WILL GIVE U 4
MA AT 5 CM AND 20MA AT 75 CM OF THE TANK LEVEL.
NOW THE SAME THING U CAN DO FOR THE COMP. MOISTURE LEVEL.
TO OPERATE SOV U HAVE TO USE THE ANALOG SIGNAL COMING FROM
DPT AND WITH USE OF THIS U HAVE TO GENERATE A DO COMMAND
(24V). THIS COMMAND WILL DIRECTLY GO TO SOV(24 V) WHEN
LEVEL IS HIGH.
SUPPOSE DPT TAG IS (PI01)
SET PI01.HH AT 75 CM.. AND USE THIS SIGNAL TO GENERATE THE
DO FOR SOV USING A SWITCH LOGIC IN DCS
| Is This Answer Correct ? | 9 Yes | 2 No |
What is basic of instrumentation
how can loop single 4-20 ma to two isolation amplifier? i mean i have two isolation amplifier with 4-20 ma input and 1-5 v output.can i done series connection ?
How to Calibrate Vibration Probe (Axial, Redial) in field
How a pH sensor & analyzer work at waste water treatment plant, whats the principle & science is beyond this,How pH sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in analyzer
How to calculate the flow rate in Vortex flow meter?What is K factor?Can you give me an example calculation to understand the same as better?
How hart protocol can be connected with control valves?
Tell me the field calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter.
What are Sinking and Sourcing IO Cards
If a flow transmitter (magnetic type FT) that can measure flow and temperature, then why in some industries people use flow transmitter and temperature transmitter in the same line 1 after another? Even after 1 single flow FT is capable of measuring flow as well as temperature.
1 Answers Process Control Technologies,
what is the difference between mmhg & mmwc?. i want to calibrate a transmitter in the range of -100 to 300 mmwc. Which is the reference for calibrate the Tx,if mmwc not available?. Is it mmhg or mmho2?.
how u calibrate sox nox co2 co in cemps?what is opacity n HPm?tell the standard parameters of cems?
Is wet leg type system nessesary to measure water level of steam DRUM? How the transmitter is calibrated to measure this level?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)