Please tell me 1 ton = How many Kilowatt (Electrical)
Answers were Sorted based on User's Feedback
Answer / chandru_williams
I would like to say that , if the 1 ton which is mentioned
here refers to refregiration or AC, then it is given as
1Tr = 1.5 KW.
This is the general thumb rule.
Is This Answer Correct ? | 147 Yes | 65 No |
Answer / b.sudhahar bagavathiappan
I have think 1 ton = 1.2 kw, HVAC design pepoles are using
that value for constrction works
Is This Answer Correct ? | 54 Yes | 16 No |
Answer / avnish sharma
1 ton = 12000 BTU/hr
and to convert BTU/hr to horsepower,
12,000 * 0.0003929 = 4.715 hp
therefore 1 ton = 4.715*.746 = 3.5 KW
Is This Answer Correct ? | 83 Yes | 50 No |
Answer / myo
a standard ton of refrigeration is 12,000 BTU/h = 200
BTU/min ≈ 3,517 W
Is This Answer Correct ? | 25 Yes | 13 No |
Answer / gulshan goyal
1 ton is a unit defined for air conditioner.it is the heat
energy consumed by 1000kg(1 ton) ice at 0 degree tempreture
to melt in 24 hours. hence it the latent heat for 1 ton ice
to change its phase to water.
Is This Answer Correct ? | 17 Yes | 9 No |
Answer / murali
1 TR refers 1 Ton(US) of refrigeration capacity. It is the
heat required to melt 1 Ton (907. 185 kg) per day of ice at
0 Deg C to water at 0 Deg C. This is basically the latent
heat of fusion of ice.
Latent heat of fusion of ice @ 0 deg C = 80 Kcals / kg
For melting 907.185 Kg ice / day, the heat required is
72575 Kcals / day or 3024 Kcals / hr or 3.516 KJ / sec.
Since 1 KJ / sec = 1 Kw, 3.516 KJ / sec = 3.516 Kw.
Is This Answer Correct ? | 12 Yes | 7 No |
why the carbon brushes are used heat created rotating parts in eiectricity
why we pefer the salient pole for synchronous motor ?
Why heat produce in AC machine higher than DC machine?
i HP = ?? 746 watts or 735.5 and how??
what is the difference between ac motor and dc generator
Whats difference between a single phase & a three phase motor?
why humming sound occured in HT transmission lines.
what do you mean by leading power factor & lagging power factor
Why does the power consumed is always constant even if a fan speed is altered?
What is the LUX
why Transformer and DG rating capacity is in KVA
why do we use 25kv supply for traction purpose