WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?

Answers were Sorted based on User's Feedback



WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?..

Answer / habeebm

AS Per IS:1554(Part1)&7098(Part1)

'A' - Alluminium
'2X' - XLPE Insulation
'F' - Steel Strip Armour
'y' - PVC Insulation
'W' - Steel Round Wire Armour
'y' - PVC Outer Sheeth
'ww' - Steel Double round wire armour
'yy' - Steel Double Strip Armour
'Wa' - Non Magnetic round wire armour
'Fa' - Non Magnetic flat strip armour

AYFY Means Alluminum PVC Insulated Fltat strip armour and
PVC outer sheeth cable

Is This Answer Correct ?    156 Yes 19 No

WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?..

Answer / gnanamoorthy

AYWY
ALLUMINIUM CONDUCTOR INNER PVC INSULATED WOUND ARMOUD
AND OUTER PVC INSULATED

Is This Answer Correct ?    37 Yes 12 No

WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?..

Answer / sushanta

Alluminium PVC innsulated steel armour round armoure wire
PVC outer sheet.

Is This Answer Correct ?    37 Yes 18 No

WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?..

Answer / rituparna das

what is the full form of cts wiring????

Is This Answer Correct ?    27 Yes 12 No

WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?..

Answer / ashish

A = Appearing as a first letter denotes Aluminium Conductor.

Y = PVC Insulation or PVC Sheath depending on the position in which it appears.

2X = 2-X (Cross-linked Polyethylene) Insulation.

W = Round Steel Wire Armouring.

WW = Double Round Steel Wire Armouring.

F = Formed Steel Wire (Strip) Armouring.

FF = Double Formed Steel Wire (Strip) Armouring.

C = Metallic Screening (Usually of Copper).

CE = Metallic Screening (usually of Copper) over each individual core.

Wa = Aluminium Round Wire & Aluminium Formed Wire (Strip) Armouring
b) Type Designations :
AYY Aluminium Conductor, PVC Insulated, PVC Outer Sheathed.

AYWY Aluminium Conductor, PVC Insulated, Galvanised Round Steel Wire Armoured and PVC Outer Sheathed.

AYFY Aluminium Conductor, PVC Insulated, Galvanised Flat Steel Wire (Strip) Armoured and PVC Outer Sheathed Cable.

AYCY Aluminium Conductor, PVC Insulated, Metallic Screened and PVC Outer Sheathed.

A2XCY Aluminium Conductor, XLPE Insulated, Metallic Screened and PVC Outer Sheathed.

AYCEFY Aluminium Conductor, PVC Insulated, individual core metallic screened, Flat steel Wire (strip) Armoured and PVC Outer Sheathed.

A2XCEFY Aluminium Conductor, XLPE Insulated, individual cores metallic screened, Flat Steel Wire (Strip) Armoured and PVC Outer Sheathed.

Is This Answer Correct ?    19 Yes 5 No

WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?..

Answer / sundaresan.m

AYWY-
ALLUMINIUM CONDUCTOR INNER PVC INSULATED WOUND ARMOUD
AND OUTER PVC INSULATED

Is This Answer Correct ?    7 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

why do you add the load short circuit impedance when considering short circuit amperage. It seems that you should only consider supply. If you need to consider loads and you don't know what loads are to be added , what would be a good sub-transient reactance rating for the loads?

0 Answers  


what is there inside an inverter and how it works?

0 Answers  


What is earth fault?

3 Answers  


what is the meaning of vcc

0 Answers  


Why the bypass and blocking diodes are used in solar modules?

1 Answers  






When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok. So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?

2 Answers  


I have carried out wiring for lighting in a shed in Industrial area which contains Metal halide lamps & have balanced in 3ph.Now when we put all the lines on in the daytime the current taken at 3phases at MCB comes to be equal i.e.28,29,28Amps respectively but in the night time i.e between 7p.m.to 11p.m. at the same MCb the current is 52,59,62Amp, though I have fit 63A MCB it is tripping in the above period.What may be the reason.? Note: This industry is located in industrial area where majority of steel ingot manufacturing plants are there. Whether this may be due to harmonic? what should I do to overcome above problem.pl suggest urgently.

4 Answers  


we have earthmat at 110KV substation.we would like to take earth resistance.b some says that by connecting earth megger terminals (C1,P1) at middile point of earthmat (at riser) will cause voltage gradient at other earthmat nods and dont get exat earth resistance.when connecting at end nods will get exat value . is it correct .please explain

0 Answers   TNEB Tamil Nadu Electricity Board,


what is the bus bar size of 2700 amp ACB breaker ? and what is the cable size ?pls detailed answer ?

3 Answers  


differentiate between one way two gang switch & two way one gang switch, used in designing the loads of building.

1 Answers  


watt meter have 4 terminals what there name??? and what theses 4 terminals indicates ?? and why 2 terminals are short circuited??

1 Answers  


Please clarify, 1. Is it required to lay two runs of GI wire along with Armoured LT cable if it is laid between one big mains (63Amps TPN SDF) to small main (32A TPN SDF) with proper glanding termination? 2. If the armoured cable with proper glanding is laid from DB to CNC machine, is it required to run two runs of body earthing to the Machine from DB? 3.If the armoured cable with proper glanding is laid from Substation to Hangar, distance is approx. 100 mtrs, is it required to do earthing at shop area though the primary termination at substation is earthed through gland.

0 Answers   HAL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)