WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?
Answers were Sorted based on User's Feedback
Answer / habeebm
AS Per IS:1554(Part1)&7098(Part1)
'A' - Alluminium
'2X' - XLPE Insulation
'F' - Steel Strip Armour
'y' - PVC Insulation
'W' - Steel Round Wire Armour
'y' - PVC Outer Sheeth
'ww' - Steel Double round wire armour
'yy' - Steel Double Strip Armour
'Wa' - Non Magnetic round wire armour
'Fa' - Non Magnetic flat strip armour
AYFY Means Alluminum PVC Insulated Fltat strip armour and
PVC outer sheeth cable
Is This Answer Correct ? | 156 Yes | 19 No |
Answer / gnanamoorthy
AYWY
ALLUMINIUM CONDUCTOR INNER PVC INSULATED WOUND ARMOUD
AND OUTER PVC INSULATED
Is This Answer Correct ? | 37 Yes | 12 No |
Answer / sushanta
Alluminium PVC innsulated steel armour round armoure wire
PVC outer sheet.
Is This Answer Correct ? | 37 Yes | 18 No |
Answer / rituparna das
what is the full form of cts wiring????
Is This Answer Correct ? | 27 Yes | 12 No |
Answer / ashish
A = Appearing as a first letter denotes Aluminium Conductor.
Y = PVC Insulation or PVC Sheath depending on the position in which it appears.
2X = 2-X (Cross-linked Polyethylene) Insulation.
W = Round Steel Wire Armouring.
WW = Double Round Steel Wire Armouring.
F = Formed Steel Wire (Strip) Armouring.
FF = Double Formed Steel Wire (Strip) Armouring.
C = Metallic Screening (Usually of Copper).
CE = Metallic Screening (usually of Copper) over each individual core.
Wa = Aluminium Round Wire & Aluminium Formed Wire (Strip) Armouring
b) Type Designations :
AYY Aluminium Conductor, PVC Insulated, PVC Outer Sheathed.
AYWY Aluminium Conductor, PVC Insulated, Galvanised Round Steel Wire Armoured and PVC Outer Sheathed.
AYFY Aluminium Conductor, PVC Insulated, Galvanised Flat Steel Wire (Strip) Armoured and PVC Outer Sheathed Cable.
AYCY Aluminium Conductor, PVC Insulated, Metallic Screened and PVC Outer Sheathed.
A2XCY Aluminium Conductor, XLPE Insulated, Metallic Screened and PVC Outer Sheathed.
AYCEFY Aluminium Conductor, PVC Insulated, individual core metallic screened, Flat steel Wire (strip) Armoured and PVC Outer Sheathed.
A2XCEFY Aluminium Conductor, XLPE Insulated, individual cores metallic screened, Flat Steel Wire (Strip) Armoured and PVC Outer Sheathed.
Is This Answer Correct ? | 19 Yes | 5 No |
AYWY-
ALLUMINIUM CONDUCTOR INNER PVC INSULATED WOUND ARMOUD
AND OUTER PVC INSULATED
Is This Answer Correct ? | 7 Yes | 7 No |
why do you add the load short circuit impedance when considering short circuit amperage. It seems that you should only consider supply. If you need to consider loads and you don't know what loads are to be added , what would be a good sub-transient reactance rating for the loads?
what is there inside an inverter and how it works?
What is earth fault?
what is the meaning of vcc
Why the bypass and blocking diodes are used in solar modules?
When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok. So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?
I have carried out wiring for lighting in a shed in Industrial area which contains Metal halide lamps & have balanced in 3ph.Now when we put all the lines on in the daytime the current taken at 3phases at MCB comes to be equal i.e.28,29,28Amps respectively but in the night time i.e between 7p.m.to 11p.m. at the same MCb the current is 52,59,62Amp, though I have fit 63A MCB it is tripping in the above period.What may be the reason.? Note: This industry is located in industrial area where majority of steel ingot manufacturing plants are there. Whether this may be due to harmonic? what should I do to overcome above problem.pl suggest urgently.
we have earthmat at 110KV substation.we would like to take earth resistance.b some says that by connecting earth megger terminals (C1,P1) at middile point of earthmat (at riser) will cause voltage gradient at other earthmat nods and dont get exat earth resistance.when connecting at end nods will get exat value . is it correct .please explain
0 Answers TNEB Tamil Nadu Electricity Board,
what is the bus bar size of 2700 amp ACB breaker ? and what is the cable size ?pls detailed answer ?
differentiate between one way two gang switch & two way one gang switch, used in designing the loads of building.
watt meter have 4 terminals what there name??? and what theses 4 terminals indicates ?? and why 2 terminals are short circuited??
Please clarify, 1. Is it required to lay two runs of GI wire along with Armoured LT cable if it is laid between one big mains (63Amps TPN SDF) to small main (32A TPN SDF) with proper glanding termination? 2. If the armoured cable with proper glanding is laid from DB to CNC machine, is it required to run two runs of body earthing to the Machine from DB? 3.If the armoured cable with proper glanding is laid from Substation to Hangar, distance is approx. 100 mtrs, is it required to do earthing at shop area though the primary termination at substation is earthed through gland.