if AVR fails in alternator. what will be the effect.
Answers were Sorted based on User's Feedback
Ans: From my real experience the voltage may not come to
zero, the volltage will fluctuate from one value to another
it may not constant at any time period. with this frequency
also increases drastically. due to this there is chance of
blown down of ACB fuses and coils.
| Is This Answer Correct ? | 32 Yes | 8 No |
Answer / v.d.vamshinath
There wont be any excitation to the main field other than
residual magnetism which is lost drastically(within
fraction of second) if AVR failed on load.
So voltage grops and may come down to zero.
If AVR fails when there is no load on alternator, the
residual magnetism will be sufficient to build some voltage
less than the rated voltage till it exists.
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / p.raju
The AVR scheme comes into operation only when there is a
change in loading.......
we have AVR scheme to regulate the changes in voltage level
at the alternator terminals, because of change in reactive
power loading.when AVR fails it will not increase the
voltage, thats why further decrease in voltage takes
place ..... which leads to final voltage collapse of the
system.
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / culla felix
when the AVR fails in the alternator there will be no device
that will control the flactuation of the output voltage the
same thing that there will be no device that will give the
voltage excitation in the field(rotor) of an alternator, only
the residual voltage will excite the field to build up more
strong fluxes, in that matter there will be no consistent
output voltage in the alternator
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / pratap k s
it depends on the alternator field excitation circuitry. In
a brushless alternator with compound excitation the
alternator produces a high voltage around 440V with the AVR
disconnected and the AVR regulates the output volatge to a
set value say 400V even if the laod varies from 0 to 100%
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / satya
alternator trip at loss of exitation because it can not
biuld up exitation voltage to the field. its null meter
becomes 0 position.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / emeka spark
I agree with Amritpal Singh Sidhu. i had similar
experience of AVR failure at the site few days ago and i
provided 12volts from the battery. innitially the voltage
was a bit higher than normal but i adjusted the governor of
the DG till i got a normal voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / amritpal singh sidhu
If AVR fails to work, then we troubleshoot the same by
providing the 12V DC from DG set battery to the field
winding of DG set. But in that case we should take care
that normal load can be put on, because the battery can not
regulate the voltage as the AVR done.
| Is This Answer Correct ? | 5 Yes | 5 No |
Answer / s f ali
Actually when AVR damages, although the engine is running on fine RPM you will not having voltages like your required. I personally observed that engine was running on fine RPM and I was getting 14 L-N voltages.......
| Is This Answer Correct ? | 0 Yes | 0 No |
Where we can use 3.5c cables instead of 4c cables.Why?
how many poles we use in high power generation
How to design pavement quality concrete by using C.R.C.P Method
how do the stepper motor works.
7- What is the Dissipation Factor and the difference between it and Insulation Resistance Test? 8- What is the task (function) of DC and AC reactors in power plant? 9- What is the task (function) of (open delta with earthed) in some types in transformers? 10- What is the base of the selection of the vector group in transformers? 11- What is the zig-zag transformer and its function by drawing in large detail? 12- What is the polarity ? 13- Why we make short between phase(R) in high side and phase (r) in low side in vector group test? Where High Side ( R ,S and T ) and Low Side ( r ,s and t ). 14- What are the time on delay and time off delay? 15- What is the vector group? 15- What is the task (function) of different types of vector group such as Dyn11 , Dd0 , YNd1,……..,?
what is the resultant phase shift in a 3 phase power system including neutral if on or more phases gets grounded or short circuited. kindly explain in detail for the reasons...
To determine the Healthiness of Insulation we will be performing Dielectric tests i.e Insulation Resistance test, Partial Discharge test,Switching Impulse, Lightning impulse, Tan Delta test ...etc why we required to perform this many test, why cant we do only one test. for Transformer, CT's
What determines the thermal loading on the motor?
WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL
Why we are not using capacitor in line when load on Genset?
How can you measure the signal from the PT100 sensor?
What is a thermocouple, and it working principle?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)