We cannot avoid inrush current when any transformer is
switched on after a long period of shutdown. Only thing we
can do is minimising it by charging the transformer by the
lowest voltage (using tapp changers)and we can avoid
spurious tripping by inrush current by using only
transformer differential relays in which an inrush current
filter is used.
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / vinothbabu.k
BRFORE STARTING ON THE TRANSFORMER WE SHOULD SWITH OFF ALL
THE OUTGOING FEEDER FROM THE DISTRIBUTED PANEL BOARD,THEN
ON THE TRANSFORMER WITHOUT CONNECTING ANY LOAD, THEN SWITH
ON THE FEEDER ONE BY ONE,R CONNECTED LOAD.THIS THE METHOD
TO AVOID THE INRUSH CURRENT FROM THE TRANSFORMER...
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / mukhesh
their is no chanses to avoid the magnetic inrush currents
in p t/f by wn inrush curens come the t/f will doing the
vibrations to avoid vibrations steel chains are fixced
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / makku
we can reduse inrush currrent by using winding having high reactance
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / priyan
You can reduce the second harmonic by using the DELTA
connection in the CT’s but I prefer to play with the
protection relay parameters, in this case it is better to
control the differential current, there is 2 slopes for the
differential zones, try to increase the slope N01 to get
passing the inrush current.
By filtering the 2 nd harmonics, refer to relay co
ordination and set the values
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / karthikeyan
Its recommended to install an CLR (Current Limiting Reactor)
befroe the Power Transformer to reduce the inrush current.
| Is This Answer Correct ? | 3 Yes | 7 No |
Answer / a.kossay
TO AVOID INRUSH CURRENT IN TRANSFORMER WE MUST USE A
VOLTAGE SENSE RELAY TO MONITOR THE VOLTAGE PEAK , SO WHEN
ITS VOLTAGE PEAK THE C.B CAN BE CLOSED AND INRUSH CURRENT
WILL BE LIMITED
| Is This Answer Correct ? | 1 Yes | 7 No |
can we use ps class in combination with protection class in differential protection and over current protection.
What is the difference between earthed & unearthed system?
how do skin effect is reduced when hallow cond or stranded cond are used ?
Working of microwave oven?
i am completed diploma in ece,and working in ht and lt lines.so is elligible diploma in ece for get electrical C Licence?plse give ur opinion?
What are all present producing cost of Per KWH of various Fuel?
whay we used silica gel in Transformer
why buchholz relay is kept on inclined position and why it is cover??
why power factor occur only inductive load not in resistive ?
Diagram on interconnectivity of 11kv transformer with RMU (i.e, one incoming and two outgoing or two incoming and one outgoing)
defination of controlled shunt reactor
why do the alternator doesnt have open circuited windings in armature???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)