What are methods to avoid the inrush current at the time of
starting of power transformer ?

Answers were Sorted based on User's Feedback



What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / suresh kumar

We cannot avoid inrush current when any transformer is
switched on after a long period of shutdown. Only thing we
can do is minimising it by charging the transformer by the
lowest voltage (using tapp changers)and we can avoid
spurious tripping by inrush current by using only
transformer differential relays in which an inrush current
filter is used.

Is This Answer Correct ?    15 Yes 1 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / vinothbabu.k

BRFORE STARTING ON THE TRANSFORMER WE SHOULD SWITH OFF ALL
THE OUTGOING FEEDER FROM THE DISTRIBUTED PANEL BOARD,THEN
ON THE TRANSFORMER WITHOUT CONNECTING ANY LOAD, THEN SWITH
ON THE FEEDER ONE BY ONE,R CONNECTED LOAD.THIS THE METHOD
TO AVOID THE INRUSH CURRENT FROM THE TRANSFORMER...

Is This Answer Correct ?    13 Yes 4 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / mukhesh

their is no chanses to avoid the magnetic inrush currents
in p t/f by wn inrush curens come the t/f will doing the
vibrations to avoid vibrations steel chains are fixced

Is This Answer Correct ?    0 Yes 0 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / makku

we can reduse inrush currrent by using winding having high reactance

Is This Answer Correct ?    0 Yes 0 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / priyan

You can reduce the second harmonic by using the DELTA
connection in the CT’s but I prefer to play with the
protection relay parameters, in this case it is better to
control the differential current, there is 2 slopes for the
differential zones, try to increase the slope N01 to get
passing the inrush current.
By filtering the 2 nd harmonics, refer to relay co
ordination and set the values

Is This Answer Correct ?    1 Yes 2 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / vijay

apply a coil before applicable circuit

Is This Answer Correct ?    3 Yes 7 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / karthikeyan

Its recommended to install an CLR (Current Limiting Reactor)
befroe the Power Transformer to reduce the inrush current.

Is This Answer Correct ?    3 Yes 7 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / a.kossay

TO AVOID INRUSH CURRENT IN TRANSFORMER WE MUST USE A
VOLTAGE SENSE RELAY TO MONITOR THE VOLTAGE PEAK , SO WHEN
ITS VOLTAGE PEAK THE C.B CAN BE CLOSED AND INRUSH CURRENT
WILL BE LIMITED

Is This Answer Correct ?    1 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

What is ferro-resonance in electrical system? Why it occurs and what are measures to prevent it?

0 Answers  


When to use Oil Transformer type and When to use Dry type? What is the difference between both?

2 Answers   ABC,


why do we provide metallic enclosure to bus duct and then ground it?

1 Answers  


What are the protection used for alternator,transformers.

2 Answers   Adani,


HOW TO CONVERT SQ MM OF A CABLE TO DIAMETER, EG. CABLE SIZE IS 185SQ.MM WHAT IS THE DIA OF THE CABLE??????????????

3 Answers   Parsons, SWAN,






Dear all: Recently we got a question about Interface between PMS and SAP-PM.once we got a update message from PMS.we should set the deletional flag for functional location in SAP system.Is there any FM or BAPI to use?There are only functional location create and change provided by SAP. Best regards!

0 Answers  


why the efficiency of the dc machine is high ,when it is operated as a generator?

3 Answers  


HAI,HOW TO SET THERMAL OVERLOAD RELAY FOR DOL STATRTER FEEDER AT START AND RUNNING?

4 Answers   L&T,


I want to give Power supply to a house from the Feeder, Total Load of the House is 128 KW, how to calculate cable size for this load ?

5 Answers  


Our transformer capacity is 500kva & voltage ratio is 11kv/433v step down tf.Now i need to know if my input voltage is 10500v and what would be the secondary side voltage i.e output voltage ?

3 Answers   Helma,


how does a liquid starter reduce the starting currents?

0 Answers  


why dc supply given to ac alternator rotor

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)