How to take Vector group test of Transformer?

Answers were Sorted based on User's Feedback



How to take Vector group test of Transformer?..

Answer / dinesh kumar

Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2,3) the vector group of transformer is
verified

Is This Answer Correct ?    225 Yes 28 No

How to take Vector group test of Transformer?..

Answer / e.saravanan

Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W2N- Which is secondary-Star connection
3.By connecting terminals 1U& 2U
4.Then three phase Supply is given to 1U-1V-1W
5.By measuring the terminal given below
We get
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
THE BELOW GIVEN CONDITION IS SATISFIED THEN DYn11 IS
CONFIRMED
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N

Is This Answer Correct ?    121 Yes 26 No

How to take Vector group test of Transformer?..

Answer / elangovan

The above method is correct

Is This Answer Correct ?    45 Yes 12 No

How to take Vector group test of Transformer?..

Answer / sajeesh

wht abt YN d11 transformer...??????

Is This Answer Correct ?    28 Yes 13 No

How to take Vector group test of Transformer?..

Answer / vinod

Vector group is punched on the name plate based on the user
requirement by the manufacture. Aim of vector group test is
at site is to check if their is any damage in the windings
during transportation and erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted for all vector group of transformer

Then to qualify the test following conditions are to be
satisfied after measurement of voltages.

nR+nY=RY, By>> Bb and Yb=Yy.

Is This Answer Correct ?    19 Yes 5 No

How to take Vector group test of Transformer?..

Answer / srinivas

can anyone say me hoe to draw vector group and what is the
use of different vector group and its application plz

Is This Answer Correct ?    18 Yes 8 No

How to take Vector group test of Transformer?..

Answer / adi

Procedure given by Mr. dinesh kumar & Mr. E.saravanan is
correct but is there any explanation for this three
conditions.
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N

Is This Answer Correct ?    13 Yes 3 No

How to take Vector group test of Transformer?..

Answer / tum

1U-1V=[1U-2N]-[1V-2N]

Is This Answer Correct ?    11 Yes 4 No

How to take Vector group test of Transformer?..

Answer / prasad talada

1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2) the vector group of transformer is
verified

Is This Answer Correct ?    9 Yes 3 No

How to take Vector group test of Transformer?..

Answer / vinay kumar

can anybody tell hw u r writing this is the vector group
calculation for this one.....
what happens if the voltages r not satisfied for the
specified vector group and if so what to do.......

Is This Answer Correct ?    7 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

at the time of starting back emf of a motor is zero.so how can it will start to run??

1 Answers  


How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99

4 Answers   Dhanalakshmi Industries, DLF,


prove that inegration of { e^z / z^2 + pi^2 }dz is equal to i/pi by Cauchy Residue Theorem.

1 Answers  


what is pulverisation

2 Answers  


what is high voltage in india?

11 Answers   Essar,






what is a composite error in current transformers, why occurs & in which it will occur i.e, either metering ct/ protection ct

0 Answers  


WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AND ITS CABLE IS 4CX50SQMM ,NOW ITS GETTING ABNORMAL HEATUP IN CABLE,PLZ TELL WHY ITS HEAT-UP?(CABLE LENGTH IS 15 METERS ONLY)

10 Answers  


what is the reason for choosing DYn11 in transformer, why not DYn12 or something else

1 Answers  


What is EHT(Abrebiation,Function,Voltage Regulation & how it works?

2 Answers   Adhunik,


What is K-rated transformer? What is the use of it? What can be the size(pls provide calculation if possible) of K- factor transformer for 550kW,690V motor operating with drive (VFD)?

0 Answers  


I have three phase 400 KW,390 A MOTOR.For this motor which type of Cable is required....specifically rubber cable required. Can anyone help me..

5 Answers  


why some transformer without breather.

1 Answers   GTS,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)