how to calculate knee point voltage of current transformer?
Answers were Sorted based on User's Feedback
Answer / rajendra soni
10 % increase in voltage gives you 50 % increase in
excitation current is called knee point voltage.
To measure this first demagnetise the CT and apply
voltage gradually from secondary keeping primary
winding open circuited. while doing this above
phenomeneo will be obsesrved.
Is This Answer Correct ? | 162 Yes | 26 No |
Answer / balamurugan r
10 % increase in voltage gives you nearly 50 % increase in
excitation current is called knee point voltage or
breakdown voltage.
To measure this first demagnetise the CT and apply
voltage gradually(like 10% or 20% step) from secondary
keeping primary should be open circuited.
Is This Answer Correct ? | 59 Yes | 13 No |
Answer / saleh abdulsalam trabelsi
to calculate knee point voltage of current transformer by
formal
Vknee point = Isecandary(Rct+ Rcable+ Rburden)
where
Rct= resistenc of current transformer
Rcable =resistenc of cable =2Rcable
Rburden =burden of relay
IF Vknee point< manufacture voltage of current transformer
current transformer is good
IF Vknee point> manufacture voltage of current transformer
current transformer must be change
Is This Answer Correct ? | 88 Yes | 47 No |
Answer / pankaj joshi
I am not familiar with the term saturation test but it seems
from the above posts like an exciting current test to
obtain the knee-point of the CT. With this test you can also
obtain the exciting curve (mag-curve) of the CT.
You'll need a variable voltage, (easiest obtain from a
variac - must be able to obtain the suitable voltage) a
voltmeter, an ammeter, a pencil and paper.You'll have to
measure the voltage and the current while you do the test.
Apply the voltage to the secondary winding with the primary
and other windings being open-circuited. Increase the
voltage until you reach a point where a small increase in
voltage results in a big increase in current.
Now slowly decrease the voltage to a few measuring points,
while you measure the current. (write it down) Something like:
205V - 1.1A
200V - 0.6A
190V - 0.238A
180V - 0.149A
170V - 0.114A
150V - 0.08A
125V - 0.061A
100V - 0.049A
50V - 0.028V
25V - 0.017A
0V - 0A
You have to decrease your voltage slowly to zero volt to
demagnetize the CT-core.
BEWARE The knee-point voltage will depend on the size and
class of the CT, and it can be very high on some CTs
(several hundreds of volts) Be very cautious, you will be
working on live equipment during the test.
Now you can just plot the current and voltage values on a
graph. This is the mag-curve of the CT. IEC classify the
knee point voltage as the point where a 10% increase in
voltage results in a 50% increase in current.
Is This Answer Correct ? | 50 Yes | 10 No |
Answer / arup
Knee point voltage, Vkn = (VA X ALF)/ In
VA= Burden =30 (Say)
ALF= Accu. Limit. Factor = 20 (Say)
In= Rated Secondar Current =5 amp (Say)
Then Vkn= 120 volts
If CT Ratio is 2000:5 then In=5
Class is 5P20 then ALF=20, P=Protection CT
Is This Answer Correct ? | 37 Yes | 10 No |
Answer / shakir mehmood
The formula for Knee Point Voltage is:
Vkp = K * If/CTR * (RCT + RL + RR)
in which,
K = Constant, conventionally taken as 2.0
Vkp = The minimum Knee Point Voltage
If = Maximum Fault Current at the location, in Amperes
CTR = CT Ratio
RCT = CT Secondary Winding Resistnace, in Ohms
RL = 2-way Lead Resistance, in Ohms
RR = Relay Burden, in Ohms
Is This Answer Correct ? | 31 Yes | 5 No |
Answer / pankaj
The knee-point voltage will depend on the size and class of
the CT, and it can be very high on some CTs (several
hundreds of volts) Be very cautious, you will be working on
live equipment during the test.
Now you can just plot the current and voltage values on a
graph. This is the mag-curve of the CT. IEC classify the
knee point voltage as the point where a 10% increase in
voltage results in a 50% increase in current.
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / dinesh
Below equation is helpful in calculating the knee-point voltage of Protection CTs
Vkp = ALF(VA / In + Rct x In)
ALF = Accuracy Limit Factor
VA = Burden
Rct= Resistance of the secondary winding
In = 1A or 5A
For example if the CT Ration is 500/1A, Burden is 20VA and Class is 5P20, then Vkp is 20(20/1) = 400V.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / arvind negi
CT Knee Point Voltage Calculation Sheet
Primary Secondary Volt
Resistance Resistance Length
In MVA In AMP In kV In ohm In
ohm/km in Meter In %
1 CT ratio of the trasformer REF Protection -
1200 1 - - - - -
2 Transformer Rating, MVA 20 - - -
- - - -
3 % Impedance, %Z - - - -
- - - 13.9
4 Voltage of Line Side, KVLV - - -
11 - - - -
5 CT Secondary Resistance, RCT (ohm) - -
- - 6 - - -
6 Resistance of control cable of 2.5 Sq. mm.
- 8.5 -
7 Loop Length of Control Cable - - -
- - - 120
Calculation:
1) Fault Current at Primary Side of CT (kA) =
MVA/*100(%Z*1.732*KLV) 7.55
2) Fault Current at Secondary Side of CT, If (A)=
6.29
3) Cable Lead Resistance, RL (Ohm)=
1.02
4) Knee Point Voltage Vk (Volt) = 2If(RCT+2RL)
101.2
REMARKS : -
Knee Point Voltage of CT provided by CGL for REF CT
= 115V and for Differental CT = 200V are in order.
Is This Answer Correct ? | 8 Yes | 4 No |
Answer / sunny
Is the answer given below is correct?
For calculating knee point voltage there are two methods,
they are
1.Low method
2.High method
1.low impedance method
Vk=24In(Rct+2Rl)
2.High impedance method
Vk=4IsRs
Then, Rs=If/Is(Rct+Rl)
where
Is,In-Rated Sec. Current of CT
Rct-CT resistance
Rl-Max. one way lead reistance from CT to Relay
Is This Answer Correct ? | 8 Yes | 6 No |
What is thyristor?
2 Diesel Generators 900KVA connected to the bus bar for essential load as an alternative for power taken from 11/440V 3KVA Transformer supplying this bus bar. my question here is in the event of power failure on 11KV side can I feed the power to 11 KV bus by using the same transformer as reverse feed, what will be the inrush current???
hr round
If a transformer primary winding operates at 240v, the secondary at 120v and the load is 1500w & the transformer is rated at 92% efficient, what's the current flowing through the primary winding of the transformer? What is the formula for finding this?
My self munna.I had completed diploma from mechanical can I join facility and maintanance companys
which braking is used in traction motor and what is its working send at mukeskumar27@hotmail.com
sir, my question is that if we start any three phase induction motor with star connection.will be current taken ? please send a formula.
How earth fault & earth leakage equvpment are works?
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<
Wht ar the reason for low voltage on consumer side?
Why open circuit test of transformers is conducted at rated voltage??Why not any other voltage??
in transformers for ex. 100mva and 400kv the secondary current is about 420 amps but for selection of bushing the capacity of selected bushing is 2000A why there is such big difference ?