how to calculate knee point voltage of current transformer?

Answer Posted / shakir mehmood

The formula for Knee Point Voltage is:

Vkp = K * If/CTR * (RCT + RL + RR)

in which,

K = Constant, conventionally taken as 2.0

Vkp = The minimum Knee Point Voltage

If = Maximum Fault Current at the location, in Amperes

CTR = CT Ratio

RCT = CT Secondary Winding Resistnace, in Ohms

RL = 2-way Lead Resistance, in Ohms

RR = Relay Burden, in Ohms

Is This Answer Correct ?    31 Yes 5 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

We need to current density & short circuit calculation at 65kA for aluminium & copper busbar.

1267


Why do we avoid electrical conduits in floors at apartments?

1635


An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor reactance at stand still is A 2 ohm B 1.25 ohm C 3.15 ohm D 2.25 ohm

1767


Why AC current leads voltage in capacitor and how?

1634


What is Anemometer used to measure?

687






Please explain, how to test vector group of tranformer(Delta y1) . Thank

1234


While performing stability test of differintial cts how to know the voltage and current on both side of the transformer?

3076


What is meant by short-pitched winding?

676


what maximum range of star & delta in hp or kw ?

1287


how to calculate the change over time for star delta starter for different KW motor?

3758


Why the frequency of ac in india is 50 hz but in some other countries it is 60 hz.

1704


sir i ve applied for hindustan petroleum and power grid india ltd..and the exams on feb 22.can you pls send model papers and tell how to prepare for those.i need to get into any of these for sure.....

1755


Show the schematic arrangement of diesel power station layout and give its principle of operation.

2550


Can we test the alignment of End shield and stator of turbogenerator without rotor insertion? Also how to fix maintain the alignment at site installation?

1810


How many turns are there in primary winding? (In Transformer)

1229