Answer / priya
starter is mainly used to limit the starting current ,which
is very much greater i.e 4 to 5 times at the time of
starting.we have to limit this.otherwise it may damage the
other equipments also.for that we are using starter ..
it limits the current by adding resistance in the circuit.
various types of starters available.
2 point,3 point,4 point types are widely used.....
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / v.selvakumar
if u r using stat delta in induction motor it will reduce
stating current .57(aprrox),in the case of d.c motor
application it limit statrting current according to emf
equation E=v-iara
ia=v-E/ra
where ra aramature is very less.normally in the order of
ohms.at starting E is zero.so ia=v/ra so current will be
high.
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / anuj kumar
During Starting Motors take a very high current i.e.-5 to 7
times of its normal rating which can cause damage the
machine due to excessive also cause a sharp voltage dip
which is unacceptable for other equipment connected to same
line.
To prevent from this high starting starters are used
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / divya
dc motors r self started motors.but as d initial resistance
is small ..by ohms law v sa dat current inc.so inord 2
reduce d inflow of current n 2 run the motor in safe zone v
vl use this starter.
v can c it in 3-pt.starter,4-pt starter.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / michael angelo borjal
The starter motor converts electrical energy to mechanical energy and is mounted on the cylinder block in a position to engage a ring gear on the engine flywheel.
Is This Answer Correct ? | 0 Yes | 0 No |
starter are use to reduce the high starting current and provide protection against under voltage & overload condition
in dc motor 3-pt & 4-pt starter are use. the resestance are ude to limit high starting current & nvc are use to other protection.
in ac motor dol ,star-delta,& autotransformer are use.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / boopathi
Starter are basically used to reduce the starting current.
I = ( V - Eb ) / R.
Where I is the field winding current,
V the voltage and Eb - Back up emf and R the winding resistance.
During starting Eb = 0, and R - a very small resistance.
so, as the high current passes through the winding, there is
chance for winding to burn out. When the motor attains the
normal speed it generate the back up emf, enough to reduce
the winding current.
To avoid this we need to reduce the voltage(V) or increase
the winding resistance. Since the reduction of supply
voltage is difficult to attain, a starter is used, which
will push high resistance during starting and gradually
reduces and fully removed from the circuit when the motor
attains the full speed.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / selva ganesh
IF YOU GIVE SUDDENLY MAXIMUM (FULL) CURRENT APPLIED ON
MOTOR MEANS THE MOTOR COIL SYSTEM WAS TOTALLY DAMAGED.SO
WILL USE THE STARTOR MEANS TO GIVE THE CURRENT IS
UNIFORMELY (CURRECTLY).
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jodha
ac motor thr rotor current dirctly proportional to slip
at the moment of starting the rotor is standstill, it means
the slip has the it is maximum value so therotor current
also maximum so,it cause rotor is burned. to avoid it we
must provide the stater.
Is This Answer Correct ? | 0 Yes | 0 No |
Difference between On Line capacitor and Station Type capacitor.
what composit error,ratio error,phase error in CT and PT??
What is voltage in two phase?
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
Wat is da difference b/w neutral earthing and unearthed system?
What is difference between YNyn0 and YNyn ??
What will be happend if we not ground CT secondary?
3 Answers Enercon, Engro, THDC,
What will happen if i replace a inductive proximity switch with photo sensor in a machine?
what is relation between torque and speed / rpm?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
Why only 1 CVT in Y-phase is used for synchronization in 3 phase power system?
Am using an electronic digital display to see the RPM of ABB ACS 550 drive, which is showing negative value when the motor & drive in stop mode but it is showing correct value during the run mode. can anyone help me out??
2 Answers Bala Power Solutions,