What is the power factor you maintain at ur organization?
Answers were Sorted based on User's Feedback
Answer / anu
all are telling its 0.9 to 1 but nobody is not telling how
ur maintain that? what are the technics using for that?
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / ronald
power factor regulation is done by connecting the Capacitor
bank- Dry type (Auto- by fixed steps or by manual
regulator) to the main Distribution board MDB.(remember the
baiscs and how cos phi is calculation is made)
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mphiremath
always pf should maintaine 0.90 to 0.96. It avoids the more
energy consumption.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / thowsif_emerson_csm team
The Power Factor Should be above 0.9 as per BESCOM
Starndard.
If the PF is bellow 0.9 then in Karanataka thier will some
amount of Penalty i.e P.F Penalty,they will add up this
amount in the monthly Electriccity Bill issued KPTCL.
So to avoid this we sholud maintain the PF Above 0.9 Lag....
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sarang hivarkar
P.F can be maintained by using HHF Harmonic Hybrid Filter (HHF) panel and APFC panel.p.f should be 0.9 to 1 required in Industry.we are used HHF panel to reduce Harmonic distortion current Harmonic in the plant and maintained the P.F.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ravi.hs
for any industry you have keep maintaining the pf @ 0.95
that is the std .
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / rajkumar n
power factor is the ratio of true power/apperent power*cos
fay is called power factor.. loads are three types
1.Resistive Load
2.Inductive Load
3.Capacitive Load
Inthis load Resistive load is Unity Powerfactor
Inductive load is Lagging powerfactor
Capacitive Load is Leading Powerfactor
PowerfactorImprovement:
1.Static Capacitor
2.Synchronous condensor
3.Phase Advansor
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / shasheen
In our orgn we are maintaining 0.98 by APFC at L.T side
and H.T Capacitors parallel to motors and H.T bus
capacitors. If our power factor is less than 0.95 in A.P
State elect board will impose fine Our running load is
35 MVA OF Cement Plant
Is This Answer Correct ? | 1 Yes | 0 No |
WHAT IS EXTENDED DELTA AUTOTRANSFORMER? WHERE WE USE THAT?
in a dc shunt motor what happens if motor takes high current,no speed
what is the electricity
HOW TO CALCULATE GROUND FAULT CURRENT IN 430V 4000AMP AIR CIRCUIT BREAKER?
what is the meaning of DY-11 Z-5%
How is operate breaker failure scheme in substation
How the real power output is controlled in a Generator?
Is it weather conditions make any problems to the electrical equipments and if yes means is it any precautions needed?
differtiate between energy consevation and energy efficiency..
I have 440v power coming to facility,( not being used ) can I buy large generator, (gas) to sell power back to electrical co.
why CT ratio stand for 50/5, 100/5, 25/5.
When a fourth resistor is connected in series with three resistors, the total resistance