what will happen when reverse reactive power occurs in
alternators?
Answers were Sorted based on User's Feedback
Answer / ramji
When reverse reactive power occurs the outgoing current in
the particular alterntor will go high and it will trip on
overcurrent.Also this conditon occurs when excitation of
the subjected alterantor fails when it is connected
parallel with other alternator or grid.Also this condition
occurs when the rotating diode of alternator fails when
them machine is ruuning.If wrong pls correct me.
Is This Answer Correct ? | 13 Yes | 5 No |
When alternator reactive power goes to negative, running
with Grid. Also alternator power factor it goes to leading.
It condition alternator will draw the reactive power from
the grid. So, we ajust the alternator reactive power always
positive side, means running MW load around 30% MVAR.
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / venu
WHEN REVERCE REACTIVE POWER OCCURE IN CONTINULY IN
ALTERNATOR THE ALTERNATOR END CONNECTION BURN OUT, THIS IS
MY PRACTICAL EXPERIENCE.
Is This Answer Correct ? | 3 Yes | 8 No |
in communication what is the role of elelctrical engineer?
How to Prepare preventive maintenance shedule of machine tool.
30 kVA and voltage 380/220VAC how to find out kA?
Our Alternator nameplate specifies a power factor of 0.8. When the Alternator is on light load, the bus bar voltage rises to 11240 volts, whereas the standard value is 10500 volts. Is it ok to increase the power factor to 0.85 or 0.9. I am afraid because the power factor on the name plate is only 0.8 ?
"TRANSFORMER MODELING AND ANALYSIS" MEANS WHAT AND WHICH TOPICS U READ IN THIS
In a single how much maximum current and watts using
why we are testing cables with DC supply not with AC supply?
9 Answers Aurobindo, DEWA, L&T,
What is the difference between air & vaccum circuit breakers?
Neutral CT for 45MVA 132/11 KV YNd11 Transformer. NCT REF CLASS-PS or 5P20 with 20VA burden which is suitable.
what is the eight bit unit?
WHY MOSTLY BATTERY VOLTAGE IS IN MULIPLE OF 2 LIKE 2V,4V,8V,16V,18V....
what is strip power factor?